Hello,

Would welcome thoughts/advice on wiring query below. Apologies for a possibly excessive amount of detail, wanted to provide as much info to aid understanding. I will post photos, can't see the button to upload them immediately.

Context: Damp 2x car garage - insulation underway to resolve that. Loft boards added for permanent storage of lightweight boxes.

Current lighting:
16a MCB type B on CU fed from house via SWA
Within garage, split into lighting and power circuits, both radial
2-plate feed to switch A at roller door end
2-way switching via pre 2006 3 core & earth to second switch B at opposite side of garage 5-6 metres away.
2x fluorescent battens in the roofspace.

Am doing more and more woodworking within the garage, and although I've currently left a gap in middle of garage for some light, the loft boards will eventually cover the roofspace and block light into the main workspace, so last year purchased 1x LED 5ft batten and 1x rectangular LED panel to fit below the joists.

2x new light fittings will be turned on routinely when coming into the garage.

2 existing roofspace battens only to be switched on when entering loft space.

Position for new LED batten is already known, so attached to joists last week.

Have run a second (new) 3-core and earth between the two switches (not yet connected at either end).

Have converted both existing 1-gang 2-way switches to 2-gang 2-way, moving the existing wiring across to match exactly.

Have connected 1.5mm T&E to batten lead through a wago box, and tacked along one of the joists to the switch wall.

Due to a complete absence of assessing (and/or forgetting) the feed location, I had planned to connect the new batten to rear switch B. Hmmm.. only one cable into switch B, the 3-core and earth from switch A. D'oh.... "Fail to plan, ... " I know, I know...

The additional rectangular LED panel, which will very likely be nearer the feed, I don't yet plan to mount until I have moved additional floorboards into position above its intended location.

So in the meantime, I'm trying to determine best option to connect the LED batten.

Current thoughts below, would welcome ideas from the pros here...

1) Create a branch from power circuit from socket nearest batten, use that as feed, but would still need to drop to switch B, and recognise it could cause light failure if the power circuit is tripped (though power and lighting all off 1x MCB anyway)

2) Use temporary task lighting, fit additional floorboards, mount the LED panel, connect it to the much nearer feed at switch A, then extend circuit to new batten - least favoured, but appreciate may be sensible

3) Run branch from feed to somewhere near switch B, connect switch B as primary 2-way for light circuit 2

4) Preferred option, if regs permit... can I run the neutral from feed at switch A, through blue-sleeved grey of 3C&E to switch B, permanent line on black or brown as usual, to connect the batten at switch B? i.e. connect the batten's live and neutral at switch B, even though feed is into switch A?

My understanding is 3C&E implicitly has a neutral but various posts I've read have different views on whether this is viable. Most of the details I've read on 3C&E suggest feed and switched line to the light fitting are only from the same switch.

Some posts seem to suggest you can't carry the neutral through on L1/L2 since the circuit will always be live and other potential issues, but the existing wiring does carry neutral through, rather than joining to light fitting neutral in a wago or loop terminal. (Recognise 2x wrongs, if it is wrong, don't make a right.)

(I'm assuming I can't just branch from existing light battens to new ones as I need to turn the 2x pairs on/off as necessary, but please advise if I've misunderstood. )

I will likely get an EICR but absolutely strapped for cash so trying to work out options first.

Thank you to those that have had the patience to read through!!
 
Photographs of 2x newly installed 2-gang 2-way switches, both having replaced earlier 1-gang 2-way. Original backbox temporarily retained on switch B. Neither old nor new switches had grommets, plan to add.)
1000006529.jpg

1000006534.jpg


1000006533.jpg


1000006525.jpg
 

Attachments

  • 1000006525.jpg
    1000006525.jpg
    3.6 MB · Views: 431
That doesn't look great, no entry grommets/sealing, earths should be connected to the front plates and one cover screw missing.
 
get it right before getting it working would be a good motto.
 
That doesn't look great, no entry grommets/sealing, earths should be connected to the front plates and one cover screw missing.
Hi @westward10, thx for prompt response. I forgot to mention missing grommets in my original post (explains all the crap in switch B) - I assume missing since house was built mid 90s, mentioned it in the reply with the photos earlier.

I'd started removing the faceplate to photograph inside when I realised an external photo might be useful (hence missing screw) - that is back in place.

Flying earth added to switch B (in photo), but agreed need to do same on switch A. Welcome the feedback, all important.
 
Hello,

Would welcome thoughts/advice on wiring query below. Apologies for a possibly excessive amount of detail, wanted to provide as much info to aid understanding. I will post photos, can't see the button to upload them immediately.

Context: Damp 2x car garage - insulation underway to resolve that. Loft boards added for permanent storage of lightweight boxes.

Current lighting:
16a MCB type B on CU fed from house via SWA
Within garage, split into lighting and power circuits, both radial
2-plate feed to switch A at roller door end
2-way switching via pre 2006 3 core & earth to second switch B at opposite side of garage 5-6 metres away.
2x fluorescent battens in the roofspace.

Am doing more and more woodworking within the garage, and although I've currently left a gap in middle of garage for some light, the loft boards will eventually cover the roofspace and block light into the main workspace, so last year purchased 1x LED 5ft batten and 1x rectangular LED panel to fit below the joists.

2x new light fittings will be turned on routinely when coming into the garage.

2 existing roofspace battens only to be switched on when entering loft space.

Position for new LED batten is already known, so attached to joists last week.

Have run a second (new) 3-core and earth between the two switches (not yet connected at either end).

Have converted both existing 1-gang 2-way switches to 2-gang 2-way, moving the existing wiring across to match exactly.

Have connected 1.5mm T&E to batten lead through a wago box, and tacked along one of the joists to the switch wall.

Due to a complete absence of assessing (and/or forgetting) the feed location, I had planned to connect the new batten to rear switch B. Hmmm.. only one cable into switch B, the 3-core and earth from switch A. D'oh.... "Fail to plan, ... " I know, I know...

The additional rectangular LED panel, which will very likely be nearer the feed, I don't yet plan to mount until I have moved additional floorboards into position above its intended location.

So in the meantime, I'm trying to determine best option to connect the LED batten.

Current thoughts below, would welcome ideas from the pros here...

1) Create a branch from power circuit from socket nearest batten, use that as feed, but would still need to drop to switch B, and recognise it could cause light failure if the power circuit is tripped (though power and lighting all off 1x MCB anyway)

2) Use temporary task lighting, fit additional floorboards, mount the LED panel, connect it to the much nearer feed at switch A, then extend circuit to new batten - least favoured, but appreciate may be sensible

3) Run branch from feed to somewhere near switch B, connect switch B as primary 2-way for light circuit 2

4) Preferred option, if regs permit... can I run the neutral from feed at switch A, through blue-sleeved grey of 3C&E to switch B, permanent line on black or brown as usual, to connect the batten at switch B? i.e. connect the batten's live and neutral at switch B, even though feed is into switch A?

My understanding is 3C&E implicitly has a neutral but various posts I've read have different views on whether this is viable. Most of the details I've read on 3C&E suggest feed and switched line to the light fitting are only from the same switch.

Some posts seem to suggest you can't carry the neutral through on L1/L2 since the circuit will always be live and other potential issues, but the existing wiring does carry neutral through, rather than joining to light fitting neutral in a wago or loop terminal. (Recognise 2x wrongs, if it is wrong, don't make a right.)

(I'm assuming I can't just branch from existing light battens to new ones as I need to turn the 2x pairs on/off as necessary, but please advise if I've misunderstood. )

I will likely get an EICR but absolutely strapped for cash so trying to work out options first.

Thank you to those that have had the patience to read through!!
Sorry im trying to follow your post but I'm getting lost half way.if you could re post it but just say what you are trying to achieve.maybe others will understand and advise you on best course of action but it's been a long day sorry .
 
Hello,

Would welcome thoughts/advice on wiring query below. Apologies for a possibly excessive amount of detail, wanted to provide as much info to aid understanding. I will post photos, can't see the button to upload them immediately.

Context: Damp 2x car garage - insulation underway to resolve that. Loft boards added for permanent storage of lightweight boxes.

Current lighting:
16a MCB type B on CU fed from house via SWA
Within garage, split into lighting and power circuits, both radial
2-plate feed to switch A at roller door end
2-way switching via pre 2006 3 core & earth to second switch B at opposite side of garage 5-6 metres away.
2x fluorescent battens in the roofspace.

Am doing more and more woodworking within the garage, and although I've currently left a gap in middle of garage for some light, the loft boards will eventually cover the roofspace and block light into the main workspace, so last year purchased 1x LED 5ft batten and 1x rectangular LED panel to fit below the joists.

2x new light fittings will be turned on routinely when coming into the garage.

2 existing roofspace battens only to be switched on when entering loft space.

Position for new LED batten is already known, so attached to joists last week.

Have run a second (new) 3-core and earth between the two switches (not yet connected at either end).

Have converted both existing 1-gang 2-way switches to 2-gang 2-way, moving the existing wiring across to match exactly.

Have connected 1.5mm T&E to batten lead through a wago box, and tacked along one of the joists to the switch wall.

Due to a complete absence of assessing (and/or forgetting) the feed location, I had planned to connect the new batten to rear switch B. Hmmm.. only one cable into switch B, the 3-core and earth from switch A. D'oh.... "Fail to plan, ... " I know, I know...

The additional rectangular LED panel, which will very likely be nearer the feed, I don't yet plan to mount until I have moved additional floorboards into position above its intended location.

So in the meantime, I'm trying to determine best option to connect the LED batten.

Current thoughts below, would welcome ideas from the pros here...

1) Create a branch from power circuit from socket nearest batten, use that as feed, but would still need to drop to switch B, and recognise it could cause light failure if the power circuit is tripped (though power and lighting all off 1x MCB anyway)

2) Use temporary task lighting, fit additional floorboards, mount the LED panel, connect it to the much nearer feed at switch A, then extend circuit to new batten - least favoured, but appreciate may be sensible

3) Run branch from feed to somewhere near switch B, connect switch B as primary 2-way for light circuit 2

4) Preferred option, if regs permit... can I run the neutral from feed at switch A, through blue-sleeved grey of 3C&E to switch B, permanent line on black or brown as usual, to connect the batten at switch B? i.e. connect the batten's live and neutral at switch B, even though feed is into switch A?

My understanding is 3C&E implicitly has a neutral but various posts I've read have different views on whether this is viable. Most of the details I've read on 3C&E suggest feed and switched line to the light fitting are only from the same switch.

Some posts seem to suggest you can't carry the neutral through on L1/L2 since the circuit will always be live and other potential issues, but the existing wiring does carry neutral through, rather than joining to light fitting neutral in a wago or loop terminal. (Recognise 2x wrongs, if it is wrong, don't make a right.)

(I'm assuming I can't just branch from existing light battens to new ones as I need to turn the 2x pairs on/off as necessary, but please advise if I've misunderstood. )

I will likely get an EICR but absolutely strapped for cash so trying to work out options first.

Thank you to those that have had the patience to read through!!
It doesn't look like 2 plate to me, it looks like standard 2 way.

You haven't a Neutral at the switch to take along with your S/L to your new light fitting.
 
Last edited:
4) Preferred option, if regs permit... can I run the neutral from feed at switch A,
As per Mainline above, none of your wires at switch A are neutral.
If you have a multimeter you can check that.
My understanding is 3C&E implicitly has a neutral
That's not normally the case

The possible wiring options are shown, for example, in the link below.
(Yours appears to be the "standard" two way switching circuit shown first)
The "alternative" way of wiring shown, where you supply power to one switch COM and take it from the other switch COM to the light, would allow one of the 3 cores to be used for Neutral, but I don't believe that's consistent with where you have L and N available at the moment.

As I'm sure you know, you can't make assumptions based on wire colours!
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
UK
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
DIY 2-plate 2-way Garage Lighting, feed through 3 core and earth?
Prefix
UK 
Forum
UK Electrical Forum
Start date
Last reply date
Replies
7

Advert

Thread statistics

Created
JesterClaypole,
Last reply from
Avo Mk8,
Replies
7
Views
321

Advert

Back
Top