From a regulations standpoint, is it a must to use a double pole switch for storage water heater? I don't seem to find it worded as such in the BS standards. The reason I am asking is I want to replace my current double pole switch with a run back timer from CP Electronics. This run back timer seems to have the neutral connected together and looks like it's not a double pole by definition.
Thanks for your help.
 
in the past, thousands of immersion heaters were installed with a FCU that only isolated L. i can't see a problem except that a falied element could trip RCD with just the N still connected.
 
You should fit the time controls after the means of isolation as the time control will almost certainly not be suitable for use as a means of isolation.


Sent from my iPad using Tapatalk
 
think davesparks gave the best solution. fit the timer after the D/P switch.
 
in the past, thousands of immersion heaters were installed with a FCU that only isolated L. i can't see a problem except that a falied element could trip RCD with just the N still connected.

Yes, and I am wondering from a regulations standpoint, is single pole still allowed for immersion heaters?
 
You should fit the time controls after the means of isolation as the time control will almost certainly not be suitable for use as a means of isolation.


Sent from my iPad using Tapatalk

Interesting idea. Never thought of that. That would be one way to ensure to meet regs.
 
I agree. One thing that just came across my mind is that with this arrangement, it is likely that the D/P switch would be left permanently in the ON position.
it needs to be to maintain power to the timer . the switch will be for isolation only, while the timer controls whether the heater is on or off.
 
Single pole isolation is fine for a TN system where neutral is deemed at earth potential. Double pole would be required for a TT system.
 
Single pole isolation is fine for a TN system where neutral is deemed at earth potential. Double pole would be required for a TT system.

Technically correct, but in practicality you don't get many 20A SP switches with the required contact gap for isolation.
 
You are correct I doubt you would find many, but the original query asked if single pole isolation is acceptable and it is so long as the earthing system is not TT.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
mobile

Thread Information

Title
Double pole switch a must for storage water heater?
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
12

Advert

Thread statistics

Created
Statick,
Last reply from
westward10,
Replies
12
Views
11,702

Advert

Back
Top