I'm doing the last leg of 2330 Level 3 in a week and I know there is a section about expected test results. I'm up on everything but the Prospective fault current; I know that you write down the highest reading out of Prospective Earth Fault/Prospective Short Circuit Current on the schedule of test results but how do you judge what it's going to be without the experience of a veteran sparky??

At the start of the exam we are given an earthing arrangement to apply other results too, how does PFC differ with different arrangements??

Any thoughts are greatly appreciated...
 
It differs according to the external earth fault loop impedance in accordance with Ohm's Law:

I=V/R

Say Ze is 0.15 Ohms, your expected PFC will be approximately 230/0.15 = 1533A or 1.53 KA

If this is a 3-phase supply then the value can be multiplied by 1.732 to calculate the PFC or by 2 if you follow the advice of Guidance Note 3.

In a TN-C-S supply the PEFC and PSSC will be around the same value.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Expected results of PFC test
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
2
Unsolved
--

Advert

Thread statistics

Created
pumpkinbreath,
Last reply from
pumpkinbreath,
Replies
2
Views
19,606

Advert

Back
Top