Hi. I've got a high earth leakage value on a main db supplying many 3phase cables. What's the best way to find the leakage values on each cable? Some of them can't be turned off. If I clamp around all 4 live conductors as they enter the db would this give me the earth leakage?
The only way you will test for leakage in this situation is by clamping the cable cores. You will have so many parallel paths to earth that clamping a CPC won’t give a meaningful reading.