hoover

Regular EF Member
Messages
92
Hi. I've got a high earth leakage value on a main db supplying many 3phase cables. What's the best way to find the leakage values on each cable? Some of them can't be turned off. If I clamp around all 4 live conductors as they enter the db would this give me the earth leakage?
 

telectrix

Disrespected Scouser
Electrician's Arms
Trainee Access
Messages
63,488
Location
cheshire/staffordshire
earthing conductors. measure the leakage current in mA. either that or isolate and IR test each phase conductor.
 

telectrix

Disrespected Scouser
Electrician's Arms
Trainee Access
Messages
63,488
Location
cheshire/staffordshire
earth leakage is a current flowing to earth via earthing /bonding conductors. this can be measured with and without loads being applied. measure first with no loads connected. then add loads one at a time to see if the reading, if any, increases. any sudden increase in the reading will show which load is causing the problem.
 

HandySparks

Mentor
Electrician's Arms
Trainee Access
Messages
4,364
Location
Hampshire
Hi. I've got a high earth leakage value on a main db supplying many 3phase cables. What's the best way to find the leakage values on each cable? Some of them can't be turned off. If I clamp around all 4 live conductors as they enter the db would this give me the earth leakage?
Yes, if you can clamp all the live conductors in a circuit (including neutral), any current detected must be the leakage to earth. (With a ring final you'll have to clamp the lives on both legs, of course.)

The difficulty will be getting a reliable leakage figure in the presence of large load currents and the magnetic influence of current in adjacent circuits.
 
K

Knobhead

The only way you will test for leakage in this situation is by clamping the cable cores. You will have so many parallel paths to earth that clamping a CPC won’t give a meaningful reading.
 

plugsandsparks

Electrician's Arms
Messages
1,626
Location
Chesterfield
How big is your leakage, i had 14amps going down the earth from the DB, all caused by a large number of old fluorescent fittings. Thought i had a cross over somewhere but did a load of pulling and tugging of wires and all checked out, except between fittings, which are at high level i have not checked
 
E

Engineer54

The only way you will test for leakage in this situation is by clamping the cable cores. You will have so many parallel paths to earth that clamping a CPC won’t give a meaningful reading.
Very true, in fact on many switchboards and/or bigger DB panels that incorporate E L protection relays on out-goers, it will be via a CT that encompasses all the cores of that cable being monitored...

Clamping the CPC is only really suitable for final circuits, or for comparison purposes on larger earthing cables. In an industrial/factory installation, as Tony stated, your not going to see any meaningful or particularly accurate values clamping only the CPC's ....
 