Hi,
Just been and looked at a job done recently by a colleague.
SWA dedicated 16A supply from a garage consumer unit to a external socket outlet and bulkhead light with external switch on an adjacent patio.
He hasnt provided any fusing down for the light and external switch.. (i.e. via an external switched fused spur, as I would have probably done)
He has posed the argument that because he has wired the switch and light in 2.5mm cable that the 16A circuit OCPD is sufficient, but I am concerned that the bulkhead light fitting and external switch have current ratings <16Amp.
He says its no different from a 13A socket outlet being protected by a 32Amp MCB on a ring final circuit, which I can't disagree with him on.
Can anyone provide some clarity on this for me please?
Just been and looked at a job done recently by a colleague.
SWA dedicated 16A supply from a garage consumer unit to a external socket outlet and bulkhead light with external switch on an adjacent patio.
He hasnt provided any fusing down for the light and external switch.. (i.e. via an external switched fused spur, as I would have probably done)
He has posed the argument that because he has wired the switch and light in 2.5mm cable that the 16A circuit OCPD is sufficient, but I am concerned that the bulkhead light fitting and external switch have current ratings <16Amp.
He says its no different from a 13A socket outlet being protected by a 32Amp MCB on a ring final circuit, which I can't disagree with him on.
Can anyone provide some clarity on this for me please?