B
billybee
so if its + or - 2% at 45'c should i expect to lose 10% thata 20x 0.53% ish over that temp range.
Today was a great day to see the temperature phenomenon.
It was about 20'C, no cooling benefit of any breeze and a mixture of sunny spells and cloud.
There were cloudy spells with generation being just a trickle, and when the sun came out power soared to 3.5kW. Then gradually the power output declined (as the panels got hotter) and settled around 3.0kW. Then a cloud would block the sun again, power would drop to 700W again, the panels cooled, the sun came out again and the power jumped back up to 3.5kW.
So I reckon that I was seeing a 15% loss of power output due to temperature.
The power-derating temperature coefficient of my panels is 0.43% per degree Celsius. So a rise of 35 degrees in panel temperature would explain the 15% drop in power output.
With ambient temperature around 20'C, the panels would appear to have been reaching 55'C after being in strong direct sun for many minutes.
well i agree there, the only other thing is on cold days i offtern get the same diffrence out of the last 21 days from 4 to 10kw production ive been out performed on 17 days by upto 23% but in saying that i have beaten him 4 times so even though were 10km apart weather could play some part may be cloudy here and raining there. thanks for the help anyway
the heat thing with what youve said above i can understand and agree with, cool down power up heat up power goes down and if that was happerning and mine was going up after some clould great, but mine never go back past the same output once it hits 2450 thats is best for that day (hot days) half an hour clould and it will drop but within minutes of clould clearing back to 2450 again and thats it.
or a dodgy panel?
to answer some questions
. but if its shading or faualty panels i would expect one string to be better than the other later in the day. after about 10am and for the times i get 2450 (hot days) both strings are on 8 amps and about 1200w. so if its a faulty panel there must be 2 one on each string.
thanks all
I've already explained in detail where your system is underperforming and what you can do about it.to answer some questions
roof pitch is ni on the same possibly a degree or two diffrent. according to what he told me we facing within a degree or two the same way. its not the drop thats my concirn its that it doesnt get high enough to drop (hot days) going of the inverter size and panel i'm loosing more like 20% of my peak and going of what the inverter and panels have peaked at could be over 25%. to get a drop you need a peak.
i do get a shadow i think early morning as the top string is always lower than the bottom for an hour or so. but if its shading or faualty panels i would expect one string to be better than the other later in the day. after about 10am and for the times i get 2450 (hot days) both strings are on 8 amps and about 1200w. so if its a faulty panel there must be 2 one on each string.
i know nothing about thermal camers, i'm changing the inverter next week and if that doesnt work will have to put a thermiter on the roof to check temps. sounds possibly heat is the problem. but its the way they react.
could we be looking at vaultage from the panels. mine is about 560v (inverter) and ive noticed a system with a sunnyboy inverter has much better outputs on hot days, sunny boys 700v also the eversolar i'm compairing with can run at 680v.
thanks all
thanks for the help, and sorry if you think i was arguing with the facts, i fully agree that i'm looseing that against the system at least 2% due to heat factors and my panels being a bit naff lol. and also some more looses due to 2 strings. i already had relized that an over sized inverter could cost me some performance and am made to fell worse now knowing i'm comparing against a system with an oversized inverter (700w) so i do realise the only way of improving is changing to 1 string (dont no how much diffrence) and blowing my panels up and getting better ones lol. so i have taken all your advice and am contacting my installer now to discuse the options. and trying to add more panels at a later date is also a no go going of the advice. so thanks you have all beeen very helpful and informative.
Hi Billybee
I have a fairly similar system to you - Powerone PVI3000out and 13 250w suntech panels in 2 strings
Have you noted the temp reading on the inverter when the power drops??
I have noted that as soon as the inverter temp reaches circa 54c the output power drops from 3300w to 2450w - the inverter display will also change from Tinv to TBoost.
Hope this Helps
Dave
massive massive help so is the 54c on the inverter the temp of the panels. is that what its telling you.
ive also relooked at the systems ive compaired with and on closer looking everyone one here was spot on with the heat situation as all the 4 system ar droping down to 85% of the max panel output on hot days weather the inverter is over or undersized. mines a bit worse at about 82%.
6 panels 165.1 (27.5)
6 panels 162.6 (77)
raing heavy, but its heat no heat and poor panels in heat. i will be keeping the inverter i have and looking at the string situation i think.
those are the temperatures at the heat sink on the inverter. I believe they need to be showing 70 degrees before derating occurswhat is this t-vin and t-boost and what does it mean, could it be the inverter telling you panels are to hot or is it the iverter telling us its to hot. obvisally we both experance the same problem on hot days and its when t-boost kicks in.
automatic power limitation control based on internal temperature monitoring to avoid overheating (heat sink temperature ≤70°C [158°F]).
they have internal fans inside the sealed unit to blow the warm air onto the heat sink / away from the components, but not external fans to blow air over the heat fins.I believe the power 1 inverters use heatsinks and cooling fins rather than an internal fan so it would do no harm to get a large fan blowing on the inverter from early before it gets warm so to limit the heat build up. It may help. The inverter is not mounted in an enclosed space or warm loft is it?
I believe the power 1 inverters use heatsinks and cooling fins rather than an internal fan so it would do no harm to get a large fan blowing on the inverter from early before it gets warm so to limit the heat build up. It may help. The inverter is not mounted in an enclosed space or warm loft is it?
Hello Billybee its my system you are comparing with and i like yourself in the early weeks of being up and running got a bit paranoid looking at other systems comparing them with mine.But later just let it get on with producing power for my household and are now enjoying EDF sending money to my bank lol.
For the other members here is my system.hilltopsolar 3.290kW | Monthly
probably am being paranoid a bit. but when you pay a lot for a system you want it 100% or and thanks for the info on your system the other week. and because i'm on the lower feed in tarrifs every kw counts. it might only feel like a couple of kws 50 days a year but it will add up over 25 lol. i was going to contact you and ask what data are you going off for your targets though. thanks