W

whazza22

Hi there

I was testing the earth loop on a bathroom light with the fan pull switch turned OFF (not double pole) and got a reading of 330 ohms.

When I turned the fan on, the reading was down to 0.60 ohms which is obviously ok.

Would this be due to the neutral not being switched from the pull switch?

Thanks
 
With the switch off, I reckon that you're measuring the loop resistance of the fan load, neutral and earth conductors.
Switch on, the Line conductor is in parallel with the fan load & neutral, so your Zs of 0.6 will be slightly less than if you measured it with the fan disconnected.
 
all depends on where you are measuring at. if you're measuring at the fan switched L, then the fan switch needs to be on
 
I was measuring at the bathroom light between perm live, neutral and earth then between switch live, neutral and earth. Both giving a reading of 300+ ohms. The insulation resistance is fine.

The fan is wired directly from the light with a perm live, switch live, neutral and earth so the fan runs after light is switched off.

As soon as I switch the fan on, the readings are all fine. It's just when the fan switch is off so I'm assuming its because the neutrals aren't switched?
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
High earth loop on bathroom light with fan?
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
5

Advert

Thread statistics

Created
whazza22,
Last reply from
tony mc,
Replies
5
Views
1,337

Advert

Back
Top