Discuss High earth loop on bathroom light with fan? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
W
whazza22
Hi there
I was testing the earth loop on a bathroom light with the fan pull switch turned OFF (not double pole) and got a reading of 330 ohms.
When I turned the fan on, the reading was down to 0.60 ohms which is obviously ok.
Would this be due to the neutral not being switched from the pull switch?
With the switch off, I reckon that you're measuring the loop resistance of the fan load, neutral and earth conductors.
Switch on, the Line conductor is in parallel with the fan load & neutral, so your Zs of 0.6 will be slightly less than if you measured it with the fan disconnected.
all depends on where you are measuring at. if you're measuring at the fan switched L, then the fan switch needs to be on
I was measuring at the bathroom light between perm live, neutral and earth then between switch live, neutral and earth. Both giving a reading of 300+ ohms. The insulation resistance is fine.
The fan is wired directly from the light with a perm live, switch live, neutral and earth so the fan runs after light is switched off.
As soon as I switch the fan on, the readings are all fine. It's just when the fan switch is off so I'm assuming its because the neutrals aren't switched?
Reply to High earth loop on bathroom light with fan? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Thinking a 240V AC relay activated by two independent light switches could be used to switch power to a shared inline extractor fan. The fan...
Need to replace an old Vent-Axia extractor fan as the pull chord no longer works. I bought this -...
Hi all, Got an awkward bathroom fan installation in a downstairs flat, concrete ceilings and (some) walls. Bathroom is already fully tiled and...
Hi I'm looking for some advice for adding a time delay on my parent's shower room fan. My parents had a section of their garage converted into a...