whazza22

Hi there

I was testing the earth loop on a bathroom light with the fan pull switch turned OFF (not double pole) and got a reading of 330 ohms.

When I turned the fan on, the reading was down to 0.60 ohms which is obviously ok.

Would this be due to the neutral not being switched from the pull switch?

Thanks
 
With the switch off, I reckon that you're measuring the loop resistance of the fan load, neutral and earth conductors.
Switch on, the Line conductor is in parallel with the fan load & neutral, so your Zs of 0.6 will be slightly less than if you measured it with the fan disconnected.
 
all depends on where you are measuring at. if you're measuring at the fan switched L, then the fan switch needs to be on
 
I was measuring at the bathroom light between perm live, neutral and earth then between switch live, neutral and earth. Both giving a reading of 300+ ohms. The insulation resistance is fine.

The fan is wired directly from the light with a perm live, switch live, neutral and earth so the fan runs after light is switched off.

As soon as I switch the fan on, the readings are all fine. It's just when the fan switch is off so I'm assuming its because the neutrals aren't switched?
 

Reply to High earth loop on bathroom light with fan? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, have an old bathroom fan. Which has two wires the black and red (line and neutral). The fan has no isolator switch and was powered when the...
Replies
3
Views
658
Thinking a 240V AC relay activated by two independent light switches could be used to switch power to a shared inline extractor fan. The fan...
Replies
31
Views
1K
Need to replace an old Vent-Axia extractor fan as the pull chord no longer works. I bought this -...
Replies
19
Views
1K
Hi all, Got an awkward bathroom fan installation in a downstairs flat, concrete ceilings and (some) walls. Bathroom is already fully tiled and...
Replies
1
Views
608
Hi I'm looking for some advice for adding a time delay on my parent's shower room fan. My parents had a section of their garage converted into a...
Replies
8
Views
975

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock