If you look at these pages from the ukpn network design guide you can see that 0.35 is a typical value for an existing 100A tncs supply.
0.35 is their maximum value for a new 100A service connected to an existing network but for a new service from a new network it is 0.25.
Other DNOs will provide an 80A service with a higher Ze.
0.35 is their maximum value for a new 100A service connected to an existing network but for a new service from a new network it is 0.25.
Other DNOs will provide an 80A service with a higher Ze.