Forget the obvious for a mo
Bare in mind my eyes are not the greatest,so will someone confirm or no
The view I have of the picture,there doesn't appear to be a screw in the bottom half of the centre connector
Here's a few to be getting on with:
hole in back of box - IP integrity compromised
no o ring seals around enclosure screws
missing gasket
missing lid
SWA incorrectly terminated: armour not secured
sheathing does not fully enter enclosure
missing swa gland
missing swa cable clips
missing banjo
PVC cable not mechanically protected
PVC cable not clipped
PVC cable entry not water tight (should enter at bottom/back of enclosure)
earth connected to swa live
missing earth sleeving
3x undersized connectors used for cable size (they look like 5A)
not sure which is the feed: possible mismatched core sizes
box not mechanically secure: only two screws
Here's a few to be getting on with:
hole in back of box - IP integrity compromised
no o ring seals around enclosure screws
missing gasket
missing lid
SWA incorrectly terminated: armour not secured
sheathing does not fully enter enclosure
missing swa gland
missing swa cable clips
missing banjo
PVC cable not mechanically protected
PVC cable not clipped
PVC cable entry not water tight (should enter at bottom/back of enclosure)
earth connected to swa live
missing earth sleeving
3x undersized connectors used for cable size (they look like 5A)
not sure which is the feed: possible mismatched core sizes
box not mechanically secure: only two screws
Just zoomed in looking for that 4th conductor (missed that one) and noticed that the SWA neutral's sheathing is nicked as well.
Aha, don't tell me feeding a swimming pool or hot tubWell spotted from the pic.
As I said before, this photo could be a good example of bad practice for the 2391 visual exam. BTW it was a DIYer that installed it if you haven't figured it out.
Aha, don't tell me feeding a swimming pool or hot tub![]()