really simple one how many sockets can I run off a 13amp fused spur, I know I could look it up in the book, but I'm trying to win an argument in a pub?
There is no restriction on the number of sockets that can be supplied from a fused spur as the cable cannot be overloaded, however on a practical basis the use of the sockets would need to be limited to a total of 13A total to avoid the fuse blowing all the time so consideration of expected load would be useful.
There is no restriction on the number of sockets that can be supplied from a fused spur as the cable cannot be overloaded, however on a practical basis the use of the sockets would need to be limited to a total of 13A total to avoid the fuse blowing all the time so consideration of expected load would be useful.