HappyHippyDad
Supporter
I have never TT'd a shed/garage I always just extend the earth from the house.
In the example of a shed/garage being supplied with SWA is the armour of the SWA earthed by the house (lets say TNCS) or by the earth rod?
Also, if the SWA is earthed by the TNCS then you have both TNCS and TT present in the garage CU. If the SWA is earthed by the TT then you have TNCS and TT present in the Main CU? Is that ok with regards potential difference between earthing systems?
ps... I realise you can extend the equipotential zone but I am just looking at a TT for a shed, this is because of the chance of an electric charging point being in the shed (as per my other thread).
Earth the armour at supply then gland in to a plastic box to isolate the earth.
Connect shed CU to Rod.
In your example there will be a plastic adaptable box near the shed. From this box there will be (for example) 10mm Twin and earth in to the garage CU. Will this earth be connected to the TNCS or TT? You will have the same issue with the TNCS and TT being in the same box/CU, is this a problem?
can't see any reason not to use the TNC-S and add a rod at the shed.
the argument for not using TNC-S is the problem caused if the supply neutral is lost. adding a rod would solve that problem. tin hat time .
Wasn’t that their intention for the 18th until they redacted it because North of the border they can’t sink rods in granite. Same issue but a shed.
At the end of the day you'll never eradicate all risk. PME has some potentially severe flaws but these are very rare.
The biggest of these being in contact with true earth and losing the supply neutral.
IMO whatever you do will always have a potential downside.
Gland the supply cable off within an all insulated enclosure. Take no other cpc into it, earth the consumer unit to the electrode.
Do you mean use a 2 core cable from insulated enclosure to garage CU? Maybe just have the insulated enclosure very close to the garage CU and just continue the 2 core of the SWA into it, perhaps directly behind it. That way you only have the 2 cores (without an earth) for a very short distance?
I'm going to extend the example now!!
If the shed/garage is going to have sockets/lights AND an electric vehicle charging point would you need to take 2 separate supplies (i.e 2 x 2 core SWA) as the charging point needs to be on it's own dedicated circuit? Or could it be on it's own dedicated circuit from the Garage CU? I would have thought the former as otherwise it's not really a dedicated circuit.
If the cable going to shed is sufficient with installation method and size for the sockets, lights and thr charger then you can supply it from the house cu. Then the shed/garage cu has seperate circuits for each of the 3 above. I would where possible have the rcd protection in the shed rather than house in this instance.
Regarding the question of terminating the SWA and ensuring you can't simultaneously touch exposed-conductive parts from two different earthing systems, I use a 25mm nylon compression gland on the shed/garage DB for the SWA rather than an SWA gland. After R1+R2 tests, I cut the armour off using the standard method, and leave the serving sheath the same length. I make sure the compression gland insert is completely on the sheath when tightened, but with not much inside. The end of the armour is enclosed within the body of the compression gland, out of the reach of fingers (from inside the board), meeting IP2x requirements. It's a lot neater than using a separate insulating box, containing a "proper" SWA gland.
I see no reason not to use a stuffing gland as long as the cable is properly secured by cleats etc.
A bit of heat shrink over the end of the cut end of the armour will keep it neat, just remember not to shrink it until after the Zs test
Apologies if this has been covered but If supplying a ev point I think youll need something like 40a (min depending on size of charging point) with no diversity allowed? (not done the course but im sure thats right) so in a normal house you'd probably split the tails into a new small board purely for the ev. Based on that if you were powering a shed that subsequently supplied an ev you might have to take that into account? If just a shed then its unlikely youll be using that much power at one time but might be worth considering??