The Ghost

You are asked to check the condition of a lighting circuit. You find on IR 4.5 Mohms on L-E. Assuming fittings were ok, i.e. not damaged/serviceable and all other tests meet regs.
Would you
A: Recommend a rewire of the lighting as it is not "fit for purpose"
B: Advise customer everything is fine and up to regs.
The customer wants you to provide 2 x 3 way light circuit on to the same lighting
Would you
A: Decline as you feel though the lighting meets regs you are reluctant to extend same as you feel later on there will be a problem and you will be found at fault.
B: Agree and extend lighting circuit.
 
Was the earth in the circuit completely disconnected , or was it still connected at the CU? And was the NE higher or lower Brucie.
 
N-E 400 Mohms, CPC connected at the CU soundly cpc continuity checked out ok ish at 1.19 ohms at furthest light. Up and down on one lighting circuit. L-N 400 Mohms
 
I would want to know what was causing the difference . Did you try drying it out with extended test to see if it improved .
 
Hi V, interested to know if this is hypothetical? Edit - just read your next post :)
I would likely be explaining to Customer that although it passes it might be on the way out and should be further investigated. If they were not interested, I would likely lose interest in the job too, nicely.
 
Dohhh! YES it was completely disconnected dont know what I was thinking about
But the question????
Well same as Wilko to be honest . If that was to deteriorate later and caused problems you could well be sorry you took the job .
As I said I would be wanting to know what was causing it before adding to that.
 
Ummm well the guy got another electrician in and the new one said not fit for purpose but my view is if it meets regs and it does, it is not for us to tell the customer it needs rewiring as that is strictly speaking sharp practice. I do not like to lead customer to work that is not necessary as that is illegal under trading standards. And anyway I run an honest business.
Did you work out what was causing the low result?
 
I agree , but in that scenario there is a big differential in the readings . It may have been a simple fix.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
How would you advise customer
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
39

Advert

Thread statistics

Created
The Ghost,
Last reply from
The Ghost,
Replies
39
Views
3,273

Advert

Back
Top