Discuss immersion heater and a shower pump in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

People who are not sure of the Current IEE Regulations should seriously consider joining a scheme provider and use the Technical Help Phone Lines they provide.[/QUOTE]


or retrain as a 6 week wonder plumber
 
People who are not sure of the Current IEE Regulations should seriously consider joining a scheme provider and use the Technical Help Phone Lines they provide.


or retrain as a 6 week wonder plumber[/QUOTE]

Don't care where they go or what they do as long as they get well away from this industry, its giving the industry a bad name.
 
So when are you going to start your painters course,
All you have to do is calculate it chap. Also BS EN 60669-1 spur out let 20 amp, protected by a 16 amp circuit breaker, at db, why would you put a fused spure in line on a dedicated supply for a IMM Heater. Isolating at the db then allows for maintenance, so what you are saying im wrong in my practice, or just over protecting, if you can say 100% yes to that then, prove im wrong. or explain yourself better.
 
why would you put a fused spure in line on a dedicated supply for a IMM Heater. Isolating at the db then allows for maintenance, .

A double pole, switched fcu beside the immersion allows for local isolation that is in view of the person carrying out the maintenance and allows a point to change to heat proof flex.
 
I under stand this, what im saying is that you would use a 20 amp db pole switch and the protective devices at the ccu would be 16 amp.
this would also give local isolation, but you would still need to isolate the circuit as you may have a loose wire in the spur.
 
I under stand this, what im saying is that you would use a 20 amp db pole switch and the protective devices at the ccu would be 16 amp.
this would also give local isolation, but you would still need to isolate the circuit as you may have a loose wire in the spur.

Can't really count an MCB switch as local isolation IMO unless the DB is within reaching distance of the DB.
 
So the 20 amp double pole switch would not give local isolation come on, of course it would, what i am saying is that the 20 amp double pole switch would not be fused but would offer local isolation, but for maintenance work the 15/16 amp protective device would give you complete isolation.
 
There's nothing wrong with any of the following methods with regards 3kw Insulated immersion heater elements operated via a thermostat.

20 amp double pole switch backed up by a 16amp mcb/15 amp 3036: this method as been around since I was an apprentice in 1984 and that's the way I was taught.

13amp switched fused spur: used this method many times.

13amp plug top: never used this method myself, but it was not against the 15th or 16th Edition Regs and not against the 17th as far as I'm aware.

Only other thing people can do is ring their scheme Technical Help Line if they can not agree with any of the above :D but make sure you mention the word Insulated
 
Tony

I read your earlier post regarding insulated water heaters and I am confused by the term insulated in this instance.
Obviously the element is not in contact with the water but the outer sheaving is copper which is in contact with the water. The regs define insulation as a non conductive material, now I know there is a barrier between the conducting part of the element & the outer copper sheath, but I'm not sure that I would class a domestic immersion heater as insulated. Although I'm open to discussion on this.

Also the IEE on site guide states that an immersion heater should be fed from a fused connection BS1363-4 but gives no reg number as a reference.
 
Andy

I'm not that technical to be honest with you mate. I'm going on what I was told by the NICEIC Engineer who pulled me on a PIR just before the 17th came into to force where I had coded a immersion heater (the domestic type) for being on a plug top. So unless someone can show me where the regulations have changed on this, I'm going to stay with what I was told.

How the terminology goes with regards to the insulated material between the inner and outer part of the element, phoning a manufacturer might verify who's right in this instance. The NICEIC don't normally get things wrong imo, but like I said if someone shows me the regulation change I'm happy to accept it.

Andy

Also, what would you say with regards to a kettle element, are they not of the same principle ?
 
Last edited by a moderator:
Andy not sure if immersions have changed, as I don't do a lot with them now but everyone I worked on you had to drain the tank before removing the element as they were immersed in the water. To be honest I tend to go with pushrod on this and think they are covered under Reg 554.3. and therefore not to be connected via a BS 1363 socket and plug.

As I don't work on them enough and someone definately told me they do not some under these set of Regs I certainly wouldn't argue with them.
 
Immersion heater

Water heating by electricity is usually done by an immersion heater mounted in the top of the hot water cylinder. The heater contains an insulated electric resistance heater and a temperature sensor. Domestic immersion heaters (usually rated at 3 kilowatts in the UK) run on the normal domestic electricity supply. Electric shower and tankless heater also use a immersion heater shielded or naked which is turned on by the water passing and turned off when the tap is closed. A group of heater working each one or together provide different heating levels. Electric showers and tankless heaters usually have since 3kilowatts to 7.5kilowatts according the voltage supply. Industrial immersion heaters (such as those used in electric steam boilers) may be rated at 100 kilowatts, or more, and run on a three-phase supply. 11
[edit] Electrode heater

With an electrode heater, there is no wire-wound resistance and the liquid itself acts as the resistance. This has potential hazards so the regulations governing electrode heaters are strict.http://en.wikipedia.org/wiki/Electric_heating#cite_note-0
 
Good points Tony, as I said I'm not clear myself.
The IEE in their on site guide usually include a reference to the regs,
In this case they do not.
 
Andy

Ill will always trust the advice of an NICEIC Engineer over the majority of members on here. IQ is another one who I trust, hes another qualified Engineer.
 
No mate you copied and pasted that to perfection, we now know what an immersion heater is, what I would like to know is if it's covered by regulations 544.3 as I think it is, but as I said I can't remember the last time I did an immersion and certainly not in the last 5 years.
 
Don't quite see the problem here.
Immersion heaters have been required to be permanently connected via a DP switch for about 30 years.

We are talking about a plug top and given it disconnects both live and neutral conductors at the same time, then it is also acceptable imo
 
Spin yes that or a FCU.

What the discussion is about that Pushrod seems to think that immersion heaters are covered by Regs 554.3 and in that set of regs 554.3.3 states that an immersion heater can not be connectedvia a plug and socket. I tend to agree with him, but as I've stated I don't normally work with immersions and when I do it is always connected up with either a 20amp double pole Switch or a Double pole 13amp FCU, and never thought of doing them by a plug or socket.

Tonys seems to think that an immersion does not come under these regs and so connecting via a socket and plug is ok.

Now I don't know this part of the regs well enough to say aye or nay, hence the discussion, which is why I think most of us use the forum as it opens up a good debate.
 

Reply to immersion heater and a shower pump in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Private tenant since 2011. First ever eicr February 23 informed via text it failed by text from electric secretary arranging appointment for...
Replies
12
Views
532
Good evening all, I’m currently part way through my apprenticeship and we are working on IB, IN, IZ and IT and volt drop today. And it got me...
Replies
4
Views
425
I'm looking at a vending hot drinks machine 2.9kW that has a thermostatically controlled hot water tank permanently attached to a water supply...
Replies
2
Views
222
I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
164
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
780

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock