rocker
Yea, that's what I'm saying. But if, as is being suggested here, we should not be testing individual circuits and should be testing at the bars, then doing this will mean that we are testing every other circuit, and not the one we have worked on. If I am testing an individual circuit, I:
open breaker
D/C line
Find N and CPC for circuit and D/C those
Test L1 and L2
Test L2 and LN
Test LN and L1
Look for missed neons
Test Ln and L1
Reconnect and enliven.
If we left all the CPCs in the earth bar, and all the neutrals in the neutral bar, and the rest of the installation is turned on, then we are going to get very duff readings from where the Neutral and Earth are connected somewhere on the other side of the main isolator (PME, anyone?).
These are my thoughts, anyway.
open breaker
D/C line
Test L1 and L2
Test L2 and LN
Test LN and L1
Test Ln and L1