Yea, that's what I'm saying. But if, as is being suggested here, we should not be testing individual circuits and should be testing at the bars, then doing this will mean that we are testing every other circuit, and not the one we have worked on. If I am testing an individual circuit, I:
open breaker
D/C line
Find N and CPC for circuit and D/C those
Test L1 and L2
Test L2 and LN
Test LN and L1
Look for missed neons
Test Ln and L1
Reconnect and enliven.

If we left all the CPCs in the earth bar, and all the neutrals in the neutral bar, and the rest of the installation is turned on, then we are going to get very duff readings from where the Neutral and Earth are connected somewhere on the other side of the main isolator (PME, anyone?).

These are my thoughts, anyway.
 
No because the breaker would be open (off) and all the wires would be disconnected from the board altogether. All the other circs will be live, but the one I'm working on will be deader than dead.
 
Are RCD's/RCBO's able to with stand a 500V test ? I refer you to GN3 test 2 on page 38 which states that simple installations should be tested as a whole, and IF a reading of less than 2M ohm is recorded then the circuits should be tested individually
 
No because the breaker would be open (off) and all the wires would be disconnected from the board altogether. All the other circs will be live, but the one I'm working on will be deader than dead.
I'd always been told not to work on a board live, even taking the cover off, because it exposes live parts.
Any parallel paths should be taken into consideration because they will be present when the circuit is used.
 
IR is a dead test, surely??? I wouldn't fancy scratching around in a consumer unit with the busbar exposed if the thing wasn't proved dead!:D
 
The busbar wouldn't be exposed. The cables for the circuit would be disconnected as I keep saying.
Surely if this is the wrong way to test, there is no need to have access to the screw terminals in the top of an MCB, so why aren't they put behind the shield that covers the busbar.

Are you guys seriously telling me that if you replace a lighting pendant that you power down the whole installation? Or do you just not bother to test/certify?

And as someone else has said, I would be very dubious about putting 500V through an RCBO. I understand testing in many circumstances from the neutral and earth bars, but I have never seen or heard of testing from the line busbar in a consumer unit. It just seems like madness to me. What do you do if you find a fault, just say 'oh, there's a fault somewhere on the system. Oh well.'?
 
I but surely it suggests that there is something not quite right on one of the circuits?

Best to ask yourself why we do the insulation test

eg
What are the effects of heat ,age, mechanical damage etc and what they mean to the results of the insulation test that is being done on your installaton
 
Does anyone/Has anyone used test method 2 in GN3 as stated in regs book 612.3, where to join the 2 Line conductors together and test to earth ? this removes the need to disconnect sensitive equipment and must be quite useful if you have a circuit full of fluorescent lights or similar.
 
Steve,
"Does anyone/Has anyone used test method 2 in GN3 as stated in regs book 612.3, where to join the 2 Line conductors together and test to earth ? this removes the need to disconnect sensitive equipment and must be quite useful if you have a circuit full of fluorescent lights or similar."

We use this method virtually all the time. I'ts very rare we can disconnect equipment.
I think you mean join the line(s) and neutral together and IR test between the live conductors (joined together) and Earth.
 
I'm not being funny, but are you confusing an insulation resistance test with an earth fault loop impedance test?

No, I'm not.

Insulation Resistance should be performed with the system de-energised and the means of earthing attached.
 
What do you do if you find a fault, just say 'oh, there's a fault somewhere on the system. Oh well.'?

You open circuit breakers or remove neutrals until you find the faulty circuit. That is why it says that below 2 Megohms requires further investigation. This is the further investigation.
 
You open circuit breakers or remove neutrals until you find the faulty circuit. That is why it says that below 2 Megohms requires further investigation. This is the further investigation.

Which, for the billionth time, is what I do to start with, because, for the billionth time, there is no need to test the full installation if you are only working on one circuit.
 
Just realised my last post comes off as really chippy, which was not what it meant to sound like. Just find it odd that we've all been taught in different ways.
 
Which, for the billionth time, is what I do to start with, because, for the billionth time, there is no need to test the full installation if you are only working on one circuit.

I'm not talking about working on an individual circuit.

I am pointing out that insulation resistance is cumulative.

And no need to apologise.
 
Last edited:

Reply to Insulation Resistance?? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I want to check the insulation of the 3-phase 400VAC asynchronous squirrel cage motor. Motor's stator windings are connected in delta. I've read...
Replies
10
Views
2K
Hi all, I was thinking to use heat shrink to strengthen usb cables where the cable enters the connector. I find the insulation starts to crack...
Replies
3
Views
623
Chaps - having problems with a new Megger MIT420/2 insulation/continuity tester 'oscillating' and failing to give stable resistance readings in...
Replies
2
Views
648
During an insulation resistance test IR at an EICR I measured 0.0014 MegOhms from line to earth. When I disconnected the neutral from the neutral...
Replies
4
Views
1K
Hey all, Ive been in and out of a huge house rewiring as the renovate it for a year of so. Every is thing done and dusted except the downstairs...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock