During an insulation resistance test IR at an EICR I measured 0.0014 MegOhms from line to earth.
When I disconnected the neutral from the neutral bar it's 116 MegOhms lowest (on the outside bollards).

However measuring from disconnected neutrals to earth all read over 200 MegOhms.

So it does not comply as measured but complies with neutral disconected.

Does anyone have an idea why? Screenshot_20230327_101216_Gallery.jpg
 
TL;DR
Interesting IR readings
You have to disconnect the neutral to do an IR test or it will be flat down.
 
  • Agree
Reactions: Risteard
Why if the rcd and the main switch are both off,I usually conduct global IR line to earth and neutral to earth and I only start to dismantle if high reading are observed
 
  • Agree
Reactions: brianmoooore
What voltage were you using for the IR test? Maybe the neutral was being pulled down to earth via surge arrestors somewhere on another circuit.
 
If I understand you right, every circuit individually achieves over 200MΩ but when the neutrals are commoned, one circuit reads 1.4kΩ L-E? Do we know what the aggregate N-E reading was at that moment? You mention bollards; presumably this means permanently-connected lighting loads (on which we preferably wouldn't be testing L-E and N-E separately.) If there was any kind of N-E fault anywhere on any circuit, commoning the neutrals with it will equally affect the line on any circuit with load. I would be wondering what if anything was disturbed that created an intermittent low IR on the neutral bar, even if it only happened to manifest while testing the line.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

newfutile

Arms
Supporter
~
Joined
Location
hemel hempstead
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Insulation resistance problems
Prefix
N/A
Forum
Electrical Testing & PAT Testing Forum
Start date
Last reply date
Replies
4

Advert

Thread statistics

Created
newfutile,
Last reply from
Lucien Nunes,
Replies
4
Views
1,816

Advert