Yea, that's what I'm saying. But if, as is being suggested here, we should not be testing individual circuits and should be testing at the bars, then doing this will mean that we are testing every other circuit, and not the one we have worked on. If I am testing an individual circuit, I:
open breaker
D/C line
Find N and CPC for circuit and D/C those
Test L1 and L2
Test L2 and LN
Test LN and L1
Look for missed neons
Test Ln and L1
Reconnect and enliven.

If we left all the CPCs in the earth bar, and all the neutrals in the neutral bar, and the rest of the installation is turned on, then we are going to get very duff readings from where the Neutral and Earth are connected somewhere on the other side of the main isolator (PME, anyone?).

These are my thoughts, anyway.
 
No because the breaker would be open (off) and all the wires would be disconnected from the board altogether. All the other circs will be live, but the one I'm working on will be deader than dead.
 
Are RCD's/RCBO's able to with stand a 500V test ? I refer you to GN3 test 2 on page 38 which states that simple installations should be tested as a whole, and IF a reading of less than 2M ohm is recorded then the circuits should be tested individually
 
No because the breaker would be open (off) and all the wires would be disconnected from the board altogether. All the other circs will be live, but the one I'm working on will be deader than dead.
I'd always been told not to work on a board live, even taking the cover off, because it exposes live parts.
Any parallel paths should be taken into consideration because they will be present when the circuit is used.
 
IR is a dead test, surely??? I wouldn't fancy scratching around in a consumer unit with the busbar exposed if the thing wasn't proved dead!:D
 
The busbar wouldn't be exposed. The cables for the circuit would be disconnected as I keep saying.
Surely if this is the wrong way to test, there is no need to have access to the screw terminals in the top of an MCB, so why aren't they put behind the shield that covers the busbar.

Are you guys seriously telling me that if you replace a lighting pendant that you power down the whole installation? Or do you just not bother to test/certify?

And as someone else has said, I would be very dubious about putting 500V through an RCBO. I understand testing in many circumstances from the neutral and earth bars, but I have never seen or heard of testing from the line busbar in a consumer unit. It just seems like madness to me. What do you do if you find a fault, just say 'oh, there's a fault somewhere on the system. Oh well.'?
 

Reply to Insulation Resistance?? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello everyone, Hope you're all well. I'm carrying out an overall/global insulation resistance test on a newly wired 3 phase installation we did...
Replies
24
Views
1K
I want to check the insulation of the 3-phase 400VAC asynchronous squirrel cage motor. Motor's stator windings are connected in delta. I've read...
Replies
10
Views
2K
I've recently has an EICR (report attached) carried out on my two bed flat because I need to rent it out for a year. The electrician has come back...
Replies
19
Views
1K
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
658
Hi All, My colleague and I are currently doing PAT/ISITEE Testing, and we've hit a snag with a bit of equipment - we've got 19" Racks for our...
Replies
8
Views
574

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top