F

freedomrun

Anyone give me some advice on IR Testing a domestic install at a socket outlet. I've been asked to replace a light fitting, so wanted to perform an IR test on the lighting circuit as part of my initial verification. The CU is packed and quite hard to access it in the cupboard it's been boxed in to. If i were to leave the Main Switch off and all the MCB's closed (on) and perform my IR test at a socket outlet between L-E and N-E only, surley this will test the whole install and be adequate for a Minor Works if the readings are compliant, i would also take into account any light switches for two way or intermediate. I would prefer to test at a socket outlet as i have'nt got to perform the testing up a ladder. Also, will this way of IR testing work on all types of boards, what if RCD's are present? Any advice appreciated - Thanks.
 
I wouldn't conduct a global IR test in this manner, if there are RCDs.
Individual circuits with the RCD switched off yes.
You can obtain adapters, to conduct tests at light fittings.
 
as spin says. i would invest in a set of lightmates. 40 odd quid, or at least get a BC ans an ES. an absolute must for Zs testing on lighting anyway.
 
An Initial Verification is carried out on a brand new circuit and an Electrical Installation Certificate generated, not an alteration to the circuit which requires a Minor Works Certificate.
 
I still need to ensure the IR test for a Minor Works comply, if they do not - then i cannot issue a MW cert.
 
I still need to ensure the IR test for a Minor Works comply, if they do not - then i cannot issue a MW cert.
You only need thiugh to test the circuit you are working on, and if you are replacing a light fitting, the ideal time to conduct the test, would be between taking the old down and installing the new.
Yes it would entail being up a ladder, but you would be up the ladder anyway changing the fitting.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
IR Testing at a Socket Outlet
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
6

Advert

Thread statistics

Created
freedomrun,
Last reply from
Deleted member 26818,
Replies
6
Views
2,050

Advert

Back
Top