I have come across a double socket where the earth terminations aren't linked together - Is this illegal (and what regulation do i look at?) or is it allowed, and I just put the loop-earth in one termination and join the unearthed socket with a length of Earth conductor?
 
do you mean that there's no manufacturers link between the 2 earth terminals? have you metered across them?
 
I have come across a double socket where the earth terminations aren't linked together - Is this illegal (and what regulation do i look at?) or is it allowed, and I just put the loop-earth in one termination and join the unearthed socket with a length of Earth conductor?
 
I have come across a double socket where the earth terminations aren't linked together - Is this illegal (and what regulation do i look at?) or is it allowed, and I just put the loop-earth in one termination and join the unearthed socket with a length of Earth conductor?
There should be an internal ling in the SO . See Earthing requirements for the installation of equipment having high protective conductor current "see 7.5 OSG Page 86 explains the whole thing in detail, Regulation 543.7.1.201 and 202 refers
 
Must admit that I've quite often wondered why there are two earth terminals on double sockets which are quite clearly linked. Suppose its quite handy to have the extra one if you are earthing the back box but if you have a RFC with a large number of double sockets, if the CPC's are in the separate terminals you are going to get a slightly higher r2 value plus extra connections with more room for error.
 
Must admit that I've quite often wondered why there are two earth terminals on double sockets which are quite clearly linked. Suppose its quite handy to have the extra one if you are earthing the back box but if you have a RFC with a large number of double sockets, if the CPC's are in the separate terminals you are going to get a slightly higher r2 value plus extra connections with more room for error.
See Post 8?
 
Must admit that I've quite often wondered why there are two earth terminals on double sockets which are quite clearly linked. Suppose its quite handy to have the extra one if you are earthing the back box but if you have a RFC with a large number of double sockets, if the CPC's are in the separate terminals you are going to get a slightly higher r2 value plus extra connections with more room for error.
the reason for 2 terminals is for hi integrity earthing, used a lot with IT equipment with high leakage currents. as he said above , osg pages 86 and 87 explain.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
Maidenhead
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
Legal Details - Sockets - Where is the requirement for separate socket earths to be linked?
Prefix
UK 
Forum
UK Electrical Forum
Start date
Last reply date
Replies
105
Unsolved
--

Advert

Thread statistics

Created
wilmer000,
Last reply from
nicebutdim,
Replies
105
Views
11,060

Advert

Back
Top