Thing is to think about like has been mentioned is the method of installation when a busbar chamber is used, the amount of switch fuses connected to it supplying various kit is usually a lot on most chambers, I have seen a 32 amp switch fuse tapped off with 6mm2 tails to it before and the chamber 400 amps, puts it into perspective really, however that said code it a 3 or even a 2 if you like and be done with it all LOL, who cares it is only a cable and it is Friday, get a beer in you
 
Why is it when some one disagrees with an installation method it is Bad Practice or not Good Practice seems to be a very misused term and this thread is a good example of it's misuse
 
Sorry Mate not got my BGB with me any chance you could quote what is says? I check tomoz
 
Just checked on my laptop bottom page Appendix 15 in BS7671, are you referring to the box that to the types of cable BS6044 Flat Twin and Earth?
 
Hi DJ
Just checked my BGB Appendix 15 Page 425 Fig 15A. Nowhere on that diagram does it state you can take a 1.5mm2 cable directly from the RFC to feed anything. I does however indicate that you could feed from the RFC providing you use a FCU fusing down to the load you wish to supply, providing you feed the FCU in 2.5mm2 and THEN proceed in 1.5mm2 cable as originally stated. The box you refer too states the type and sizes of cable to be used.
Pete
 