Discuss Lighting tripping rcd in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
yes rcd working fine.
Cant think of anything else.
I belled out the wire between the fitting and N and all was ok.
this light also dos not work ,so makes me think if i link this N up to this fitting it will give me te radial ?
what ya think ?
swap the fitting with the one that works and see if the RCD trips then if so take out the suspect fitting leaving the one that works in and terminal block where the suspect fitting was so the circuits complete less the fitting
Think methodically,the more you stress out about it,the less likely you are to find the fault and repair,so deep breath,and start by halving the circuit,disconnect all conductors to furthest point say,leave in place from ccu to that point,still trip?no,then that half is ok,then move further down circuit,i dont know how much experience of fault finding you have,but once you have found and fixed it,you will say to yourself that was easy,are these all existing fittings and wiring or has it been altered and now does not work?
Reply to Lighting tripping rcd in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
I sorted the fault fairly quickly as it happens but only because I'd come across it once before and at the time a few people said it couldn't...
Hi, I seem to have an RCD that keeps cutting the power at random times without actually tripping, if I reset it, the power comes on and will stay...
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
DIY query Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up. This...