SirKit Breaker
A long shot but have you tested the RCD?
Discuss Lighting tripping rcd in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Having just read this thread - what testing would have put the OP on the right track more quickly?
Would continuity test at each lighting point between L and N, and then Insulation resistance tests between lighting N and all the other circuit neutrals have worked in showing the problem?
[Just trying to be prepared for when it happens to me ]
isolate power ,turn off mcbs
disconnect circuit causing problem(L and N)
switch on borrowed load
check between circuit causing problem(L or N) to other neutrals(one by one)
until you get your reading
that should trace it-might be easier ways
You wouldn't do continuity tests first? On a completely unknown circuit wouldn't that be the thing that would tell you about the state of all the conductors and eventually that there was a problem with the neutral
and not sure what you mean by "switch on borrowed load" (and how do you know which to turn on)
Am i right in thinking that the problem was a live from a lighting circuit to a light fitting and then returning to the CU via another circuit (socket ring?)
Eco-tech - did this fault just show after a CU change or...
had someone been doing a bit of DIY bodging?
just intrigued as to what had happened previously - cheers
Reply to Lighting tripping rcd in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net