Having just read this thread - what testing would have put the OP on the right track more quickly?

Would continuity test at each lighting point between L and N, and then Insulation resistance tests between lighting N and all the other circuit neutrals have worked in showing the problem?

[Just trying to be prepared for when it happens to me :D]
 
Having just read this thread - what testing would have put the OP on the right track more quickly?

Would continuity test at each lighting point between L and N, and then Insulation resistance tests between lighting N and all the other circuit neutrals have worked in showing the problem?

[Just trying to be prepared for when it happens to me :D]

isolate power ,turn off mcbs

disconnect circuit causing problem(L and N)

switch on borrowed load

check between circuit causing problem(L :edit) to other neutrals(one by one)

until you get your reading

that should trace it-might be easier ways
 
Last edited by a moderator:
isolate power ,turn off mcbs

disconnect circuit causing problem(L and N)

switch on borrowed load

check between circuit causing problem(L or N) to other neutrals(one by one)

until you get your reading

that should trace it-might be easier ways

You wouldn't do continuity tests first? On a completely unknown circuit wouldn't that be the thing that would tell you about the state of all the conductors and eventually that there was a problem with the neutral :confused:

and not sure what you mean by "switch on borrowed load" (and how do you know which to turn on)

Am i right in thinking that the problem was a live from a lighting circuit to a light fitting and then returning to the CU via another circuit (socket ring?)

Eco-tech - did this fault just show after a CU change or...

had someone been doing a bit of DIY bodging?

just intrigued as to what had happened previously - cheers
 
You wouldn't do continuity tests first? On a completely unknown circuit wouldn't that be the thing that would tell you about the state of all the conductors and eventually that there was a problem with the neutral :confused:

and not sure what you mean by "switch on borrowed load" (and how do you know which to turn on)

Am i right in thinking that the problem was a live from a lighting circuit to a light fitting and then returning to the CU via another circuit (socket ring?)

Eco-tech - did this fault just show after a CU change or...

had someone been doing a bit of DIY bodging?

just intrigued as to what had happened previously - cheers

take this problem here where you know which pendant is borrowing -we said more or less the same thing
-first disconnect circuit

-bulb out, check between the pendant neutral(with a wander lead) and other circuit neutrals

- bulb in place and switched on you can check between the circuit phase at the board and other circuit neutrals

thats what i'm thinking,never had this problem
 
Cheers - Reckon i'll just hope my probs are more straight forward - Last time out it took me ages to discover that owner had put a curtain rail screw thru a cable supplying his outside lights which he hadn't used for 6 months. Should have been an easy one but not helped by faults on the garden lights as well - mistakenly thought that the problem was just outside:eek:
 

Reply to Lighting tripping rcd in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I sorted the fault fairly quickly as it happens but only because I'd come across it once before and at the time a few people said it couldn't...
Replies
13
Views
356
Hi, I seem to have an RCD that keeps cutting the power at random times without actually tripping, if I reset it, the power comes on and will stay...
Replies
7
Views
500
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
377
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
DIY query Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up. This...
Replies
0
Views
450

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock