Engineer54
But yes, 0.00 Megohms does not equal 0 ohms!!
So what sort of ohm value would you equate a Zero reading on a modern digital IR or MFT tester??
But yes, 0.00 Megohms does not equal 0 ohms!!
It won't be Zero, that would be a dead short, and things would have been going Bang!!
but I expect that domestic installers don't bump into mineral wiring much. The only reason I can think of why the house was wired with mineral is that the whole thing is very solidly built - concrete floors and roof for example - so probably built for an "engineer"Thanks for all your input, I will discuss with my Sparks and report back.
As I understand it the test was from Neutral to Earth - I'm presuming that is why its not going bang?!
My Sparks is certainly not young, and has come across it beforebut I expect that domestic installers don't bump into mineral wiring much. The only reason I can think of why the house was wired with mineral is that the whole thing is very solidly built - concrete floors and roof for example - so probably built for an "engineer"
So what sort of ohm value would you equate a Zero reading on a modern digital IR or MFT tester??
My MFT on 500V IR test resolves to 0.000 Meg, so in effect that's 1K. Quite often I'll then use the continuity setting (<2k) and see readings of a few ohms (at which point my continuity buzzer will work quite happily).
Potentially, this could catch the unwary as a resistance of say 1k ohms would fail an IR test but not always pull sufficient current for ADS, even with an RCD, so you could actually see 0.000 on your IR test result and still have a 'working' circuit.
and please be my guest Lucien in continuing to do so....Got caught out with a similar set of results a few years ago. Very low IR readings at the first EICR carried out on an MI installation in a church were found to be caused by widespread seal failure, rather than the odd one or two bad ends. Early 60s job, reasonable standard of workmanship with all 660V cable neatly dressed and terminated, about 20 circuits with lots of 7 core 0.002 in the lighting. We had planned to test it and if generally OK as we expected, replace the Bill Vertex DB and make localised repairs as needed.
Initial IR tests were all disappointing so we started breaking some circuits down into single runs. IIRC about 1 in 3 runs was <1MΩ, the leaky seals were spread all over the building not just the obvious damp and inaccessible areas. Because it was all imperial cable and would be a very slow job to remedy, plus the likelihood of further problems, we agreed with the customer that rewiring was the most sensible option and we started pulling in FP as soon as they could get an emergency faculty granted.
It seems one or more of the installers was not fitting and filling the pots properly, they had many decades of letting in moisture before this first test was done. I was disappointed because I have great faith in MI and had not experienced this level of widespread failure before. I would gladly have redone it all in new MI but time was against us!
and please be my guest Lucien in continuing to do so....
poor potting is not poor MI is it....