Hi everyone. i was helping/learning on a job today where the company was installing a new 3 phase distribution board in a shop. they isolated the incoming cable (incomer had an isolating switch as was a submain) and installed the new board. i was being shown how to test it and got some readings i saw that i dont understand.

with supply dead there was continuity between earth and neutral, and also got 0.00 on an insulation resistance reading between neutral and earth. could someone explain this to me please?
 
If the installation is TN-C-S, the earth and neutral are linked.
As Tony has said, if the neutral is not disconnected by the main switch, you will have continuity, unless you disconnect either the main earth or the neutral.
You should not really be conducting an IR test between conductors that have continuity.
You an also have continuity between earth and neutral on TN-S installations, as often the rest of the network may be TN-C-S, and continuty may be via another installation.
 
Last edited by a moderator:

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
neutral earth continuity
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
5
Unsolved
--

Advert

Thread statistics

Created
sparks1653,
Last reply from
sparks1653,
Replies
5
Views
7,977

Advert

Back
Top