The issues to which you can legitimately raise objections have already been covered: Power and lighting should be split across both RCDs, so loosing one bank of circuits will ensure either power or light remains in any given area of the home. Cables (including incoming tails) should be suitably supported and restrained - there are many ways in which this can be done, including the simple cable clip. If there is sufficient space for finger access where tails come in the bottom, then this should be filled. Cables should be protected from metal edges as they come into the board, which can be remedied through the use of grommet strip.

The above are the ONLY issues that you could pull the original electrician on. As well as the bit of the circuit that has not been rewired. Be advised that you must give the original electrician the opportunity to fix those issues before going down the withholding payment or part payment route.
These are also the only things that you need rectified to make the installation totally compliant and safe for continued use. So as far as safety is concerned get the above fixed and you are fine to leave everything as it is.

You do not need a new board - It would just have been "better" if you had at least been given the option of an RCBO setup, But that ship has sailed as it were. There is zero recourse on the people who quoted for you when you simply asked for a fuse board upgrade or indeed if it was part of other works for not offering the RCBO option....It's just that most of us on here find it strange due to the fact that the cost difference these days is minimal and it is "best practice" but not really laid out in black and white in the regulations.

I
 
This maybe me being a bit picky but

How long are those tails ? the ones going through those big holes near the twisted rcbos 🤣
Less than a metre, they go straight through to DP isolator in the external meter box. Considering the testing was completed at 3pm and the board install was complete including the labelling by 4.45pm I'd say it's not bad at all. Let's see a pic of one of your boards now ?😃
 
Less than a metre, they go straight through to DP isolator in the external meter box. Considering the testing was completed at 3pm and the board install was complete including the labelling by 4.45pm I'd say it's not bad at all. Let's see a pic of one of your boards now ?😃

I did mean to go back and finish this one, but the fella wouldn't let me back in.


Consumer-Unit-Replacement.jpg
 
Also unlikely to gain any benefit from the additional expense of changing to RCBOs and sourcing new busbar. I'd be inclined to leave the current set up in place, unless cumulative earth leakage happens to cause nuisance tripping (of which there have been no reports so far).
I have been advised that a dual RCD board is bad, and that I should have RCBO's - you guys are the experts, if its a matter of safety, i'm happy to swap.

There has been no tripping. I allowed extra space for the solar/car charger, but thought,
The above are the ONLY issues that you could pull the original electrician on. As well as the bit of the circuit that has not been rewired. Be advised that you must give the original electrician the opportunity to fix those issues before going down the withholding payment or part payment route.
These are also the only things that you need rectified to make the installation totally compliant and safe for continued use. So as far as safety is concerned get the above fixed and you are fine to leave everything as it is.

You do not need a new board - It would just have been "better" if you had at least been given the option of an RCBO setup, But that ship has sailed as it were. There is zero recourse on the people who quoted for you when you simply asked for a fuse board upgrade or indeed if it was part of other works for not offering the RCBO option....It's just that most of us on here find it strange due to the fact that the cost difference these days is minimal and it is "best practice" but not really laid out in black and white in the regulations.

I
Thank you, however the law says that the work must be carried out with skill and care. The test is whether a ‘reasonably competent member of the profession’ would leave it like that.

Everyone here said it’s sloppy and poor. If you boards look like this then I’d be interested to see ?

He didn’t use a torc screwdriver nor did he do any testing. I know as I was there.

The tails inside are just free floating and hanging - no clip to hold them in place, is that legal?

The cables come through the back via the metal, there is no grommet or plastic to protect the cables against the sharp metal edge again is that legal ?

The socket has a massive hole there, my finger could easily fit in there, is that legal ?

The
 
The above are the ONLY issues that you could pull the original electrician on. As well as the bit of the circuit that has not been rewired. Be advised that you must give the original electrician the opportunity to fix those issues before going down the withholding payment or part payment route.
These are also the only things that you need rectified to make the installation totally compliant and safe for continued use. So as far as safety is concerned get the above fixed and you are fine to leave everything as it is.

You do not need a new board - It would just have been "better" if you had at least been given the option of an RCBO setup, But that ship has sailed as it were. There is zero recourse on the people who quoted for you when you simply asked for a fuse board upgrade or indeed if it was part of other works for not offering the RCBO option....It's just that most of us on here find it strange due to the fact that the cost difference these days is minimal and it is "best practice" but not really laid out in black and white in the regulations.

I
I’ve given him the option to fix, he has refused. You will see his excuse in the first page. Apparently a nicely wired consumer board causes a hum and an electronic field. Lol. Now I’ve refused to pay it looks like he will come and do it, and we will go from there.

I wonder why no one quoted for a RCBO, including him. Here everyone says they quote for full rcbo.

Safety comes, so from people saying it should be a RCBO now I will change it, people are saying it’s unnecessary,

Out of interest is a car charger and solar more likely to trigger the RCD ? For £100 + labour I can put them in the board on RCBO’s.

Other than wiskas product is there a way to extend the cables in a fuse board ?

Cheers.
 
Safety comes, so from people saying it should be a RCBO now I will change it, people are saying it’s unnecessary,
Well cheers for ignoring my and others very clear advice. that advice extends to untidy fuse boards too. there is NO obligation nor regulation which states that work should be neat and tidy. The advice was RCBO's are a "nice to have" as opposed to a must have so again you will be paying twice as you have zero recourse to the installation of the board as it currently stands aside from the gaps where the tails come in.
I don't mean to sound confrontational but I/we have essentially told you where you stand legally and we have also told you that although not "ideal" the use of a dual RCD board with mcb's is NOT against ANY regulations.

I do wish you well in your endeavours. I will leave it to others to answer any further questions as im not a fan of writing out a load of words for them to be ignored. Personally I and a few others are just trying to save you cash while ensuring the installation is at least safe.
 
If he has refused then your option is to get a independent spark in to write you a report of his findings. Has we give out advice not hear say, if he takes you to court no doubt he will then you will have evidence against him.send him all copy's of the findings ask the indpendant spark to quote regulation numbers and bobs your uncle antie.
Which court I'm in to day old Bailey.
 
I am in the process of quoting a new consumer unit where the client will need a larger consumer unit

She is going for a dual RCD with additional RCBO's for, I will be installing a Hager VML91620CUSPD
She is also getting PV and probably battery storage - this is the reason for the larger unit

Hager also do a change over switch to allow the use of a seperate generator / inverter

This has dual RCD's, and is configurable as well. I still install dual RCD units as I prefer Hager but add 2-3 RCBO's as well

I would suggest you put the lower lights, lower sockets and kitchen sockets on RCBO's

If you had the larger consumer unit (VML90610CUSPD / VML91014CUSPD / VML91620CUSPD) you could remove the lower consumer unit and have all stuff on the same consumer unit
 
Well cheers for ignoring my and others very clear advice. that advice extends to untidy fuse boards too. there is NO obligation nor regulation which states that work should be neat and tidy. The advice was RCBO's are a "nice to have" as opposed to a must have so again you will be paying twice as you have zero recourse to the installation of the board as it currently stands aside from the gaps where the tails come in.
I don't mean to sound confrontational but I/we have essentially told you where you stand legally and we have also told you that although not "ideal" the use of a dual RCD board with mcb's is NOT against ANY regulations.

I do wish you well in your endeavours. I will leave it to others to answer any further questions as im not a fan of writing out a load of words for them to be ignored. Personally I and a few others are just trying to save you cash while ensuring the installation is at least safe.
Thanks Diddy but as you will see others have a different view - to the extent some don’t fit them.

Out of interest is this how you leave them ? Would you put your name to it ?
 
New posts

Reply to New rewire and fuse board - views on work. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have been asked to change cu from old fuse board which has 6 fuses. Only 4 fuses are used. The first fuse feeds cooker circuit. This is not used...
Replies
17
Views
906
In a property with two consumer units one for the ring main etc., and the other for the 1970s storage heaters (storage heater CU looks like it’s...
Replies
14
Views
1K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
I'm getting an old fuse board upgraded in an office block. The electrician has just told me that most of the circuits don't have earth cables...
Replies
44
Views
4K
Hello, I’ve got an issue driving me crazy and can’t get anyone to figure it out as it’s not their issue. We had a new extension, single rear...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top