No earth in lighting circuit what next?

Discuss No earth in lighting circuit what next? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
7
Im sure this has probably been asked before in this forum but ive just upgraded a fuseboard today and found no earth in the lighting (two core). Obviously the next thing to do would be to tell the customer either rewire or change everything on that circuit to class 2 fittings and accessories, but in this case the customer didnt want to go ahead with either.... what should i do? Cutting the circuit out would be abit extreme?
 
This is exactly how it is in reality.

Crazy that we aren't leaving the lighting circuit any less safe than when we arrived, and we have made the house owner aware of the potential dangers and made all the other circuits much safer and as a result could actually save peoples lives as you suggested, but some consider this to be the action of an unprofessional electrician.

I honestly don't believe for a second that many electricians do a full and detailed inspection of every single light switch and light fitting including the external lights and loft lights as well as every possible test on each circuit at every point along it before they quote for a C/U. Clearly some suggest that just opening the fuseboard will tell you the lighting circuits have a CPC which confirms Jack S**t, and perhaps they are also able to establish when looking inside the fuseboard if the lighting circuit has a borrowed neutral.

I apologise for so many posts on this subject, although I still haven't made as many posts since joining in December 2017 as the guy who joined just 8 days ago (lol),
You are there to make the installation safer not partially safe.
 
I think the main issue here is if he had done a few basic tests he would have found the lighting had no doc.
At that point he should have had a conversation with the client, if they refused to have it rectified he should have walked away. Instead he as swapped the Db and then energised a dangerous circuit. And sèems to have adopted a don't care attitude.
Playing devils advocate here, surely the circuit in question, having been isolated for inspection and dead testing should not be reenergised after finding such a problem? Technically the circuit should have been left isolated and an electrical danger notice issued even if the CU change where never to proceed?
As the last electrically skilled person to touch the circuit, the blame, should anything go wrong could still be on your head....
This is purely theoretical but it makes me think maybe walking away isn’t always the best course of action.
 
Playing devils advocate here, surely the circuit in question, having been isolated for inspection and dead testing should not be reenergised after finding such a problem? Technically the circuit should have been left isolated and an electrical danger notice issued even if the CU change where never to proceed?
As the last electrically skilled person to touch the circuit, the blame, should anything go wrong could still be on your head....
This is purely theoretical but it makes me think maybe walking away isn’t always the best course of action.

We, as competent sparks have no legal rights to disconnect circuits.....
 
You are there to make the installation safer not partially safe.

Sorry but that's not very sensible. We can't always completely solve every issue in life 100% and we rarely do. If a doctor could resolve the majority of a patients medical conditions, accept for just one (he wouldn't make that condition any worse) would he not bother sorting any of the other medical conditions out because he can't solve every single one. Oh I forgot the doctor doesn't come under the same criteria as an electrician, so that isn't relevant.

So if we can only make the installation 90% safer than it was, then just leave it and do nothing unless we can make it 100% safer. If you said that to an intelligent person they would think you were on a wind up.
 
The case for the prosecution:

The you the electrician did refuse to change a BS3036 board because the lightening circuit didn’t have a CPC. The net result is that my client is now dead, the result of a fatal shock from the socket circuit.

How do you plead?

Defendant: Not guilty!

Prosecution: So why is your plead not guilty?

Defendant: Because of the wording of BS 7671, I wasn’t permitted to upgrade the fuseboard, because the client couldn’t afford a partial rewire...

Prosecution: so you wouldn’t improve most of the installation which would have almost certainly prevented the death of my client

Defendent: yes sir

Prosecution: so you are saying BS 7671 prevents you making an installation safer

Defendent : er ........
All the defendant would need to do would be to reply to the last question along the lines that the installation was in a condition that could only be remediated by work in compliance with the 18th Edition. There is NO responsibility on the electrician to force the client. If the client decided not to pay for the work then their inevitable death was as a result of their own actions. Easy Peasy
 
My thoughts for what they are worth. No offence intended to anyone but based on experience.

1 : The principle issue here is does the work undertaken comply with the Regulations or failing that any subordinate guidance ?

2 : Failing 1 above if there is no guidance or Industry best practice, has the installation been left in a safe state

Given my understanding and what I have read the answer to both is No, and can only be NO because there are both BS7161 requirements as well as Industry best practice that set out clearly and unambiguously what should be done.

The answer to both of the questions above would be used in Court by the Prosecution in the event of an accident or injury/loss, and any defence would need to demonstrate without question that the installation was safe and without danger. The legal eagles deal only in facts and would not even entertain a "in my opinion" argument unless it was given by an expert witness. What would an expert witness say in these circumstances ? I think we all know.

It would be for the Installer to demonstrate that through his actions he has not left the installation in a unsafe condition and frankly I do not think he has. Once having started the installer has both the legal and moral responsibility to do the work to the correct standards Departures from Standards, etc are fine as long as you can demonstrate that they improve or are at least no more dangerous than the solutions in BS7161 or Industry best practice.

If the installer has "ended up" in this situation because they have not assessed the condition of the installation and obtained adequate information prior to the work starting then sorry but the problem is down to them to resolve through agreement with the client unless contractually the installer has have covered this eventuality in the Contract or Quotation, in which case they can rely on this to disconnect and leave disconnected any affected ccts - with suitable warning notices documented to the client.

The problem then becomes the client's not the installers.

Unfortunately the Installer has met someone who for whatever reason is holding out against paying anymore money for the work and further the installer appears to have no Contractual basis upon which to claim for additional unforeseen work.

Now the Installer could disconnect the cct but were the client to put litigation in place, it could be argued by an adept Barrister, that the work should not have commenced and that it was actually now in a less safe condition because it does not meet the current Regulations and best practice has not been followed. This would leave the installer to carry out remedial work at their expense and no doubt pay substantial compensation to the client. Then of course there is the debate about whether the installer's Insurance Company would be happy that the installer has acted with due diligence.

Even thinking of going into a legal situation on the basis of some of the justifications put here would be suicidal as any competent Barrister would tear them to pieces. Basically once your mouth was opened with one of those the only debate would be how many zeros were to go on the cheque

FWIW I think the only option now left is for the installer to formally notify the client that during the course of the work, unforeseen conditions have been discovered that require the cct to be left disconnected or for the client to pay for the necessary remedial work to bring the system into compliance with BS716 or industry best practice. The client should be reminded that they have a legal obligation not to endanger any person in their property as well as a contractual obligation to the Insurance Company to maintain the property in a safe condition.

One possible alternative to disconnect would be to through-wire any metallic fittings thus leaving the cct intact but the affected equipment in situ. The client could be asked to check to see if the remedial work is covered under their insurance as this may be a means of unlocking the deadlock.

Out of interest is there no standard form of contract for small companies/sole traders that can be followed, something which would deal with such eventualities and disputes ??

you yourself should be up before the magistrate for using as font size that is dangerous to my ageing eyesight. only joking. can't insert a smiley for some reason.
 
Playing devils advocate here, surely the circuit in question, having been isolated for inspection and dead testing should not be reenergised after finding such a problem? Technically the circuit should have been left isolated and an electrical danger notice issued even if the CU change where never to proceed?
Hi - If this was discovered during an EICR it would be coded and communicated. But if there was no active fault, would it be left isolated?
 
So if we can only make the installation 90% safer than it was, then just leave it and do nothing unless we can make it 100% safer. If you said that to an intelligent person they would think you were on a wind up.
That is not how the legal mind would work. Whether or not the system was safe or not prior to working on it is completely irrelevant here.

The installer is a skilled person and thus has the responsibility to ensure that the system is safe NOT safer than it was before, but 100% safe after they have completed work on it. If you dispute this call your Insurance Company on Monday and ask them if you are still covered if you switch back into service an installation that is not compliant with BS7671.

BS7671 and the Industry best practice is absolute determination on this and it will be those documents that would be used by a Prosecution. You can only safely depart from BS7161 if in doing so you can demonstrate that what you have done achieves as a minimum the same level of safety.

Once the installer has identified the situation and the client will not pay for it to be done then you cannot issue and IEC and without an EIC you cannot re-energise.
 
Last edited by a moderator:
That is not how the legal mind would work. Whether or not the system was safe or not prior to working on it is completely irrelevant here.

The installer is a skilled person and thus has the responsibility to ensure that the system is safe NOT safer than it was before, but 100% safe after they have completed work on it. If you dispute this call your Insurance Company on Monday and ask them if you are still covered if you switch back into service an installation that is not compliant with BS7671.

BS7671 and the Industry best practice is absolute determination on this and it will be those documents that would be used by a Prosecution. You can only safely depart from BS7161 if in doing so you can demonstrate that what you have done achieves as a minimum the same level of safety.

Once the installer has identified the situation and the client will not pay for it to be done then you cannot issue and IEC and without an EIC you cannot re-energise.

Please remember ... we have no legal rights to lock off or disconnect ...... to believe anything else is wrong
 
Last edited by a moderator:
All the defendant would need to do would be to reply to the last question along the lines that the installation was in a condition that could only be remediated by work in compliance with the 18th Edition. There is NO responsibility on the electrician to force the client. If the client decided not to pay for the work then their inevitable death was as a result of their own actions. Easy Peasy

At least their death will be their own fault so we are in the clear (praise the lord) and easy peasy,
 
Elliot I have only glanced at this thread (sorry if I repeat any thing already said)
The fact that you have noticed the metal light fittings/no cpc after the upgrade is irrelevant. You cover yourself by informing the customer of your findings in writing/txt. Label the CSU with ref to no CPC and be happy in the thought you have made it safer with additional RCD protection. The customer owns the installation at the end of the day and thus can make a decision.
 
That is not how the legal mind would work. Whether or not the system was safe or not prior to working on it is completely irrelevant here.

The installer is a skilled person and thus has the responsibility to ensure that the system is safe NOT safer than it was before, but 100% safe after they have completed work on it. If you dispute this call your Insurance Company on Monday and ask them if you are still covered if you switch back into service an installation that is not compliant with BS7161.

BS7161 and the Industry best practice is absolute determination on this and it will be those documents that would be used by a Prosecution. You can only safely depart from BS7161 if in doing so you can demonstrate that what you have done achieves as a minimum the same level of safety.

Once the installer has identified the situation and the client will not pay for it to be done then you cannot issue and IEC and without an EIC you cannot re-energise.

BS7161
Specification for propeller shaft ends and bosses for inboard-engined pleasure craft

What has this got to do with electrical installations
 
That is not how the legal mind would work. Whether or not the system was safe or not prior to working on it is completely irrelevant here.

The installer is a skilled person and thus has the responsibility to ensure that the system is safe NOT safer than it was before, but 100% safe after they have completed work on it. If you dispute this call your Insurance Company on Monday and ask them if you are still covered if you switch back into service an installation that is not compliant with BS7161.

BS7161 and the Industry best practice is absolute determination on this and it will be those documents that would be used by a Prosecution. You can only safely depart from BS7161 if in doing so you can demonstrate that what you have done achieves as a minimum the same level of safety.

Once the installer has identified the situation and the client will not pay for it to be done then you cannot issue and IEC and without an EIC you cannot re-energise.
Thank you Sir for this clarification
Absolutely 100% safe when work is compled not safer.
 
The installer is a skilled person and thus has the responsibility to ensure that the system is safe NOT safer than it was before, but 100% safe after they have completed work ...
Once the installer has identified the situation and the client will not pay for it to be done then you cannot issue and IEC and without an EIC you cannot re-energise.
Hi - appreciate if you can expand on what is considered "100% safe"?
If I extend a power circuit I ensure the existing and new bit meets the various requirements of the latest regulations. But I don't look at any other circuit in the installation. Moving on to a Consumer Unit change I would touch every circuit, so by extension I am responsible for the entire installation's compliance and safety. Your thoughts appreciated :) .
 
We, as competent sparks have no legal rights to disconnect circuits.....
Well you must be a chuffing wizard then bud. Don’t see how you can change a cu with it still connected.

Please remember ... we have no legal rights to lock off or disconnect ...... to believe anything else is wrong
Load of bull bud, ever heard of safe isolation or is that illegal in your world.
 
What is the difference? ???
When you change the CU it is mandatory to issue an EIC .
You don't just issue it but you make sure all circuits connected in that board work and comply with BS 7671.
You are required to ensure your work complies with BS7671.
There is no requirement for you to ensure the rest of the installation complies.
There is not even a requirement for you to test the rest of the installation. If anything BS7671 prohibits you from testing the rest of the installation (see the notes on the EIC form).
There’s a section in the EIC for comments on the existing installation.
NOTE: See Regulation 132.16.
The person responsible for the addition or alteration, or a person authorized to act on their behalf, shall record on the Electrical Installation Certificate any other defects observed during the course of the works that may give rise to danger.”
 
My thoughts for what they are worth. No offence intended to anyone but based on experience.

1 : The principle issue here is does the work undertaken comply with the Regulations or failing that any subordinate guidance ?

2 : Failing 1 above if there is no guidance or Industry best practice, has the installation been left in a safe state

Given my understanding and what I have read the answer to both is No, and can only be NO because there are both BS7161 requirements as well as Industry best practice that set out clearly and unambiguously what should be done.

The answer to both of the questions above would be used in Court by the Prosecution in the event of an accident or injury/loss, and any defence would need to demonstrate without question that the installation was safe and without danger. The legal eagles deal only in facts and would not even entertain a "in my opinion" argument unless it was given by an expert witness. What would an expert witness say in these circumstances ? I think we all know.

It would be for the Installer to demonstrate that through his actions he has not left the installation in a unsafe condition and frankly I do not think he has. Once having started the installer has both the legal and moral responsibility to do the work to the correct standards Departures from Standards, etc are fine as long as you can demonstrate that they improve or are at least no more dangerous than the solutions in BS7161 or Industry best practice.

If the installer has "ended up" in this situation because they have not assessed the condition of the installation and obtained adequate information prior to the work starting then sorry but the problem is down to them to resolve through agreement with the client unless contractually the installer has have covered this eventuality in the Contract or Quotation, in which case they can rely on this to disconnect and leave disconnected any affected ccts - with suitable warning notices documented to the client.

The problem then becomes the client's not the installers.

Unfortunately the Installer has met someone who for whatever reason is holding out against paying anymore money for the work and further the installer appears to have no Contractual basis upon which to claim for additional unforeseen work.

Now the Installer could disconnect the cct but were the client to put litigation in place, it could be argued by an adept Barrister, that the work should not have commenced and that it was actually now in a less safe condition because it does not meet the current Regulations and best practice has not been followed. This would leave the installer to carry out remedial work at their expense and no doubt pay substantial compensation to the client. Then of course there is the debate about whether the installer's Insurance Company would be happy that the installer has acted with due diligence.

Even thinking of going into a legal situation on the basis of some of the justifications put here would be suicidal as any competent Barrister would tear them to pieces. Basically once your mouth was opened with one of those the only debate would be how many zeros were to go on the cheque

FWIW I think the only option now left is for the installer to formally notify the client that during the course of the work, unforeseen conditions have been discovered that require the cct to be left disconnected or for the client to pay for the necessary remedial work to bring the system into compliance with BS716 or industry best practice. The client should be reminded that they have a legal obligation not to endanger any person in their property as well as a contractual obligation to the Insurance Company to maintain the property in a safe condition.

One possible alternative to disconnect would be to through-wire any metallic fittings thus leaving the cct intact but the affected equipment in situ. The client could be asked to check to see if the remedial work is covered under their insurance as this may be a means of unlocking the deadlock.

Out of interest is there no standard form of contract for small companies/sole traders that can be followed, something which would deal with such eventualities and disputes ??

Great analysis and I totally agree. The paragraph beginning FWIW aligns with my approach but I think putting the onus on the client like that is a very good move (as well as being correct) especially with regard to the insurance. This may be the way out for the poor OP. Grab it with both hands mate.
 

Reply to No earth in lighting circuit what next? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock