I've tried to research and form a plan without asking on here, but I'm just going around in circles.

Just completed an EICR. The wiring ranges from new metric colours to old imperial cable.

There are 2 lighting circuits, both containing class 1 fittings. Most of the fittings have a CPC, but there is no continuity to the MET in the consumer unit.

The CU is extremely cluttered and I simply can't be sure if there is actually a CPC leaving the CU with the lighting circuits. I cannot gain access to the beginning of the conductors where they leave the sheath. One of the lighting circuits has imperial cable in the circuit breaker, the other has metric (tinned copper). Meaning the cable is 51+ years old assuming no imperial was used after 1972 and tinned copper being replaced by untinned from 1967-1970

I realise this is clearly a C2, but is the only solution to rewire?

If the wiring system is pre 1966 and no CPC was required, I don't believe there is any requirement in BS7671 to automatically have it upgraded to current wiring standards. Of course there are now class1 fittings. Will removing these class 1 fittings then bring the code to a C3? Again, there are CPC's to most lights, my worry would be that a DIYer would simply put up a class1 light again, even with a danger note on the CU.

I really can't see this being an option, but I just wanted to be sure before I tell the customer they need a partial rewire.

Cheers all.
 
The issue is the time to identify the CPC fault versus simply biting the bullet and rewiring.

You might be able to use a wander lead around the switches and lamps and establish that most CPCs are linked, and just the CPC to some junction missing so one run of 4mm might fix the lot, but that would be a very optimistic outcome!
...and that it could soon end up costing more than a circuit rewire, a bit of a gamble and you're still left with the old wiring.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

HappyHippyDad

Esteemed
Arms
Supporter
-
Joined
Location
Gloucestershire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Solution to a C2 - No CPC on lighting circuit
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
15
Unsolved
--

Advert

Thread statistics

Created
HappyHippyDad,
Last reply from
ipf,
Replies
15
Views
3,462

Advert

Back
Top