chris d

had my mcs inspection last wk and was pulled on mounting sunny boy inverter on mdf. was told it had to be non combustable material, can anyone recommend what to use and where to get it from.
 
It's part of building regs, must be 1/2 hour fire resistant. Some MDF can be (check first).
 
What's wrong with mounting direct on to wall

Sent from my HTC Desire using Tapatalk

Quite often there isn't a wall in a loft to mount to, so normally you span a couple of stays and secure to this and the ceiling joists.
 
NICEIC told me that an inverter does not need to be mounted on a nun-combustible material and that the waterproof chipboard that I use is perfectly adequate. I use waterproof because I'd hate to see it blow with damp (unlikely I know) and it comes in 8ft x 2ft lengths easy to chop up to make boards. I have the builders merchant chop the tongue and groove off but the boards are cheap and readily available.

It would be a shabby inverter that could set fire to the board upon which it is mounted !!!

I was asked the same question during my NICEIC inspection hence me asking their technical helpline for an answer.
 
We nearly failed our NICEIC inspection because we'd been told by NICEIC that we didn't need non combustible board then were told at inspection that it should have been non combustible. Fortunately we had some fire proof plasterboard and 10 mins later all was sorted. It does say in the SMA installation manual that it needs to be non-combustible - we found that bit after the inspection :-)
 
Hi There,
You need to go to Timber Merchant and ask for 18mm MDF Class"O" or Class II ""Medite", This is Fire Retardant and complies to BS469, it has a 12mm red section in centre ,sandwiched by 3mm each face. Ask for a copy of the Data Sheets/Testing Reports (that will keep NICEIC Happy)
I pay £60 for an 8 x 4 ft sheet,

Google Search "Medite"??

Hope this helps?
I Think a lot of People will get pulled on this, NICEIC will ask you to go back and change all boards fitted

DH
 
It is, as always, open to a little bit of interpretation.

Part B Building Regs cover Fire. Table A1 defines specific parts of the structure and how the regulations apply to each part. Table A2 then gives fire protection times required for different types and sizes of building and p61 gives some guidance on how Table A2 should be applied.

It is open to interpretation as to whether a simple piece of board holding electrical equipment is covered by any of it. But, given that the manufacturers state non-combustible material should be used, I don't see any issue with playing safe and using material that is 30 minute fire rated which would be the figure for a residential dwelling with a height no more than 5m. More than 5m would require 60 minutes.
 
Thanks for trawling through Part B. I cannot see a clear direct requirement from the building regs, particularly in a loft surrounded by other combustible material (trusses/rafters). As you say open to interpretation. But of course you are right that the manufacturers' instructions (for the ones I have looked at anyway) are unequivocal on the matter. So not much discussion really.

Regards
Bruce
 
Last edited:
TRY phoning your local planning office and ask them for guidance afterall they are the ones issuing the building warrent get get them to do their job and keep copy for NICEIC if if the LA say its ok As for trawling through the building regs and interpritation One LA may interperate differently from another best check with them Unless you want to get their backs up and next time you want a warrent they check every nut and bolt IMO
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
non combustable board
Prefix
N/A
Forum
Solar PV Forum | Solar Panels Forum
Start date
Last reply date
Replies
16

Advert

Thread statistics

Created
chris d,
Last reply from
edexlab,
Replies
16
Views
11,432

Advert

Back
Top