Could someone please explain the rules when it comes to altering older installations. Ie adding sockets and downlights to old wiring and non rcd (17th edition) consumer units. Should we always advise to update non compliant parts of the installation if they are not willing (can't afford to change fuseboard) to change things. In a lot of cases people just want simple things changed and as an electrician I'm not 100% what we can and can't do. And if they want a certificate can we supply one even though their installation doesn't meet current regs??? All help greatly recieved.
 
all the work that you do must comlpy with current edition of BS7671. e.g. if you fit an extra socket to an installation that has no RCD, then you must install RCD if required, either to potect just your work or the whole of the circuit you have altered. also ensure earthing and bonding are present and adequate.
 
Basically if you put in a new piece of cable however short it will require rcd protection unless surface fixed. Your minor works cert or EIC should make mention of shortfalls of the rest of the installation but any wor you do has to comply with the current regs.
 
Basically if you put in a new piece of cable however short it will require rcd protection unless surface fixed. Your minor works cert or EIC should make mention of shortfalls of the rest of the installation but any wor you do has to comply with the current regs.

or installed in earthed metal conduit (or at a depth of >= 50mm - but that seems unlikely :smiley2:)
 
Could someone please explain the rules when it comes to altering older installations. Ie adding sockets and downlights to old wiring and non rcd (17th edition) consumer units. Should we always advise to update non compliant parts of the installation if they are not willing (can't afford to change fuseboard) to change things. In a lot of cases people just want simple things changed and as an electrician I'm not 100% what we can and can't do. And if they want a certificate can we supply one even though their installation doesn't meet current regs??? All help greatly recieved.

You give customers a choice of not having a certificate??
 
Could someone please explain the rules when it comes to altering older installations. Ie adding sockets and downlights to old wiring and non rcd (17th edition) consumer units. Should we always advise to update non compliant parts of the installation if they are not willing (can't afford to change fuseboard) to change things. In a lot of cases people just want simple things changed and as an electrician I'm not 100% what we can and can't do. And if they want a certificate can we supply one even though their installation doesn't meet current regs??? All help greatly recieved.

Yehah! Ride'em Cowboys.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
Old installations and alterations.
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
6

Advert

Thread statistics

Created
Monkeyblaine,
Last reply from
MarkieSparkie,
Replies
6
Views
1,744

Advert

Back
Top