Sbc

Should one insist to the customer to have a PIR before proceeding with a CU upgrade? if not what do you do if there are hidden nastys ie bad IR readings?
Thanks
 
No not at all.

All you can do is point out to the customer (eg on your quote) that should any faults be found due to not having a EICR done then the cost of finding them shall be at £--- per hour plus materials.
 
You don't I am afraid in Schemie world as I call it you tell the customer they need an EICR before the board change but in the real world you do a survey ie global IR and some other tests. I have done an EICR for some customers and then offered to upgrade the CU at a reduced price either way I still make the same money
 
How do you do a global IR?
I only really do by circuit through fear of damaging equipment but your way must save loads of time?
Main double pole switch off.
All circuit breakers on
Link neutral bar to line busbar (do make sure main switch is off!)
Test IR from L+N to E.
Entire installation tested.

RCDs and RCBOs may not like this (and be damaged) so you may need to split down so you are not testing through them.
If you are unsure about damaging equipment (although with a L+N to E, you should not be able to damage any equipment) then test at 250V first and if you get a low reading then something is wrong.
 
These questions may sound dumb but i really am new to this.
The regs say investigate IR <= 2mohm but for you guys personally, what low reading would stop you doin a fuse board upgrade? is there a point where you say #thats a rewire!
 
These questions may sound dumb but i really am new to this.
The regs say investigate IR <= 2mohm but for you guys personally, what low reading would stop you doin a fuse board upgrade? is there a point where you say #thats a rewire!

Be careful. A global IR test will give a lower overall "picture" than testing all circuits individually PLUS why recommend a rewire when it could be one cable/accessory which is at fault??
 
Showers give a lower reading
Ballests in Florescent light can be damaged - and give a low reading
Dimmers can be damaged and give a low reading
Neons give a low reading

I always do a IR test on 250v first between L and N to see if anything is plugged in still, not always visible between L+N and E especially on Class 2 equipment but still could be damaged by 500v.
 

Reply to PIR before a Consumer Unit upgrade in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock