i did a test on a property, found lighting circuit wired in 1.5 2 core T&E, no cpc. Under the 17th edition this circuit would need a cpc. On the PIR form
I filled in requirement 2 - needs attention. does this then need to be changed, immediately? Or can i state to the customer it is acceptable provided no changes are made to the light switches and fittings?

Are we obliged to ensure if we have done a test that must be 17th edition compliant?
 
i did a test on a property, found lighting circuit wired in 1.5 2 core T&E, no cpc. Under the 17th edition this circuit would need a cpc. On the PIR form
I filled in requirement 2 - needs attention. does this then need to be changed, immediately? Or can i state to the customer it is acceptable provided no changes are made to the light switches and fittings?

Are we obliged to ensure if we have done a test that must be 17th edition compliant?

Then its 2c not T/E

If there are no class one fittings then a C3 but if there are then a C1/2

A note should be recorded on the EICR and a label attached to the CU that no class 1 fittings should be installed.

The installation does not have to be made 17th dition compliant as it may have been installed to an earlier edition which does not neccesarily mean its unsafe.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Pir test
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
1

Advert

Thread statistics

Created
AD 543,
Last reply from
truckster,
Replies
1
Views
2,083

Advert

Back
Top