Hi folks,

My client have a generator set rated 450KVA, 220Vac, 3P, 60Hz. Recently, the during start up of operation, the generator shut down because of an unknown trouble. When I check the power analyzer (I used for monitoring), the event that caused the shut down was "PF" which means, POWER FACTOR. Now, my client said that they have a 100Vac, 6 Khz rated machine. I just want to make sure that is there a possibility that the machine rated at 6 Khz did some trouble to the generator that caused it to shut down? Does high frequency loads affect the Power Factor of the supply? Or since the rating of the supply is only 60Hz that it shut down?

Please help me on these one.
Thanks a lot guys.


Best regards,

keynotez
 
Thanks for the reply dept. It was really rated at 6KHz according to my client. I think they connect it to a step down transformer, 220 input from generator and 110 output to the machine. That will be checked tomorrow. Now, let's get back to the topic, would the 6Khz rated machine caused the shut down of the generator set? Did it caused to drop the frequency of the generator? :(
 
To be honest K most of us here would have worked on 50Hz and a few of us have on 60Hz especially us who are overseas. I,m sue some like tony may have on the 400Hz, but I think I would be safe to say I have never even heard of 6Hz let alone work on it,

You sure this is not part of a postcode??
 
Thanks for the reply dept. It was really rated at 6KHz according to my client. I think they connect it to a step down transformer, 220 input from generator and 110 output to the machine. That will be checked tomorrow. Now, let's get back to the topic, would the 6Khz rated machine caused the shut down of the generator set? Did it caused to drop the frequency of the generator? :(

It shouldn't matter what frequency the connected machine runs at, as it will be, being supplied via a double wound transformer, i dare say the machine will also have other integral isolation protection. After all the machine will probably be rated at 110v/60Hz on it's primary side o things ...It doesn't do any damage to the mains supply does it, when so connected. Then it shouldn't do anything to the generator!! By the way, is this a new machine, has the generator run with this 6KHz load without incident previously??

What other equipment and loads are connected to the generator??
 
Thanks for the reply malcolm... That machine with 6Khz rating will be checked by tomorrow. Sir, what do you mean of a postcode? I'm sorry if I'm not yet much knowledgeable about that. The only event that appeared on my POWER ANALYZER before it shut down is the POWER FACTOR that's why I'm gathering ideas which caused the POWER FACTOR to fail. What would it be? :(
 
Malcolm got it right I’ve only worked up to 400Hz. What is the rating of the 6KHz machine in KVA? Is it a static converter or a motor generator set?
 
It shouldn't matter what frequency the connected machine runs at, as it will be, being supplied via a double wound transformer, i dare say the machine will also have other integral isolation protection. After all the machine will probably be rated at 110v/60Hz on it's primary side o things ...It doesn't do any damage to the mains supply does it, when so connected. Then it shouldn't do anything to the generator!! By the way, is this a new machine, has the generator run with this 6KHz load without incident previously??

What other equipment and loads are connected to the generator??


Thanks for the great idea ENGINEER54. I will confirm all your concerns to my client by tomorrow. I will be glad if you will still support me by tomorrow. Thank you Sir.
 
Malcolm got it right I’ve only worked up to 400Hz. What is the rating of the 6KHz machine in KVA? Is it a static converter or a motor generator set?

Thanks for the back-up Tony. I will check the machine tomorrow for further clarifications. Thank you Sir.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Please HELP me (POWER FACTOR ISSUE)
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
9
Unsolved
--

Advert

Thread statistics

Created
keynotez,
Last reply from
keynotez,
Replies
9
Views
959

Advert