Can I connect a power shower supply to an existing circuit via an FCU or under the regs does it need a seperate circuit
 
When you say powershower what exactly do you mean. Is it just a booster pump located remote from the shower in the loft or something or is it a full on high powered electric job? Give us some more info mate;) happy to help.

Cheers................Howard
 
When you say powershower what exactly do you mean. Is it just a booster pump located remote from the shower in the loft or something or is it a full on high powered electric job? Give us some more info mate;) happy to help.

Cheers................Howard

It's a wall mounted power shower fed by domestc hot and cold.I don't want to run it off a main circuit ony to have it fail an inspection
 
i would usually try to put in a separate circuit but if this is not possible then i would spur off a ring main.


Can you still do that ? I am a plumber and I've done it before but with all the new regs I'm not so sure.
 
I wouldnt myself if you put in a 9.5kW shower thats maximum is 41 amps not much good on a ring that has a 32amp MCB in the CU. Besides you want to be whiter than white for your assessment.


Chris
 
I wouldnt myself if you put in a 9.5kW shower thats maximum is 41 amps not much good on a ring that has a 32amp MCB in the CU. Besides you want to be whiter than white for your assessment.


Chris

who mentioned 9.5kw. He asked about power shower not electric. Power showers draw low current no more than a couple of amps
 
plumber came to mine said sorry chap no power sower for you as i have a combi boiler .. so i fixed my old redring zeta 10.9k wifey is happy again ... plumber said its illigal to have powershower on combi..

as long the circuit is RCD if not spur off to a rcd switched spurbox ... should be in regs then ..
 
Last edited by a moderator:
Power showers can of course be taken off another circuit.

And not only a ring final circuit.

No reason why a lighting circuit can't be used if necessary.
 
just looked at some diagrams for powershowers.

C) Electrical
1. The electrical installation must be in
accordance with current BS. 7671
(I.E.E. regulations).
2. The unit should be connected into a switched
3 amp double pole fused spur, with a
minimum contact gap of 3mm in each pole.
The switch must be fitted outside the
bathroom.
Alternatively, a double pole ceiling switch, with
a pull cord and a minimum contact gap of
3mm in each pole could be used inside the
bathroom.
For additional safety, it is recommended that a
residual current device be used with either of
the above switches.
3. The earth continuity conductor of the
electrical installation MUST BE effectively
connected electrically to all exposed parts of
the appliances and services in the room in
which the water heater is to be installed in
conformity with the current BS. 7671 (I.E.E.
wiring regulations).
WARNING : THIS APPLIANCE MUST BE
EARTHED.
4. We recommend using 1.0mm2 Twin and Earth
cable for this application. Connect the mains
cable in to the terminal block, ensuring that all
power is switched off before connecting to the
mains supply.
Recommended order : -
a) Strip back wire approximately 6.0mm.
b) Ensure wires are secure in the correct
terminal block holes.
c) Ensure that the mains cable is securely
clamped in the cable clamp provided
on the backplate.
5. Schematic wiring diagram.

schem ... DP switch nothing at all about RCD .. but the regs do say anything in zone 0,1,2 use RCD 30ma
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Power shower wiring
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
20

Advert

Thread statistics

Created
jonnygarlic,
Last reply from
davelerave,
Replies
20
Views
26,745

Advert

Back
Top