J
jonnygarlic
Can I connect a power shower supply to an existing circuit via an FCU or under the regs does it need a seperate circuit
When you say powershower what exactly do you mean. Is it just a booster pump located remote from the shower in the loft or something or is it a full on high powered electric job? Give us some more info mate;) happy to help.
Cheers................Howard
It's a wall mounted power shower fed by domestc hot and cold.I don't want to run it off a main circuit ony to have it fail an inspection
i would usually try to put in a separate circuit but if this is not possible then i would spur off a ring main.
Can you still do that ? I am a plumber and I've done it before but with all the new regs I'm not so sure.
I wouldnt myself if you put in a 9.5kW shower thats maximum is 41 amps not much good on a ring that has a 32amp MCB in the CU. Besides you want to be whiter than white for your assessment.
Chris
Chris
who mentioned 9.5kw. He asked about power shower not electric. Power showers draw low current no more than a couple of amps
plumber came to mine said sorry chap no power sower for you as i have a combi boiler .. so i fixed my old redring zeta 10.9k wifey is happy again ... plumber said its illigal to have powershower on combi..
as long the circuit is RCD if not spur off to a rcd switched spurbox ... should be in regs then ..
Power showers can of course be taken off another circuit.
And not only a ring final circuit.
No reason why a lighting circuit can't be used if necessary.
just looked at some diagrams for powershowers.
C) Electrical
1. The electrical installation must be in
accordance with current BS. 7671
(I.E.E. regulations).
2. The unit should be connected into a switched
3 amp double pole fused spur, with a
minimum contact gap of 3mm in each pole.
The switch must be fitted outside the
bathroom.
Alternatively, a double pole ceiling switch, with
a pull cord and a minimum contact gap of
3mm in each pole could be used inside the
bathroom.
For additional safety, it is recommended that a
residual current device be used with either of
the above switches.
3. The earth continuity conductor of the
electrical installation MUST BE effectively
connected electrically to all exposed parts of
the appliances and services in the room in
which the water heater is to be installed in
conformity with the current BS. 7671 (I.E.E.
wiring regulations).
WARNING : THIS APPLIANCE MUST BE
EARTHED.
4. We recommend using 1.0mm2 Twin and Earth
cable for this application. Connect the mains
cable in to the terminal block, ensuring that all
power is switched off before connecting to the
mains supply.
Recommended order : -
a) Strip back wire approximately 6.0mm.
b) Ensure wires are secure in the correct
terminal block holes.
c) Ensure that the mains cable is securely
clamped in the cable clamp provided
on the backplate.
5. Schematic wiring diagram.
schem ... DP switch nothing at all about RCD .. but the regs do say anything in zone 0,1,2 use RCD 30ma
Yep.. done one recently.
Electric shower conversion to pumped mixer shower.
Used the old 6mm for the old 8.5KW electric shower, into an FCU, fused at 3amps, and from the RCD side of the board. Flex cable from the pump into the load side of the FCU.
Was very convenient as the old shower cable ran through the airing cupboard anyway, where the new shower booster pump was installed. :p
This may sound silly but how come they are only small ampage? Is it just a pump that pumps the water out? Whereas an electric shower heats the water too?
you have it correct there. The power shower usually has a small transformer powering a pump. Thats it.
C) Electrical
bathroom.
bathroom.
the above switches.
EARTHED.
mains supply.
on the backplate.
You may want to read this again ;)
electric showers -'power' and 'instantaneous' should have rcd protection
rules or no rules
Power shower wiring
jonnygarlic,
davelerave,