Hello,

I'm glad I've found this forum :)

I'm doing PIR for a customer and everything was going fine until I saw there was one 2.5mm cable leaving from consumer unit to feed 4 sockets.

The cable leaves the consumer unit and the passes threw a double pole isolator switch, it was wired this was so they could control effects lights.

At the consumer unit the radial is on a 20A MCB.

Now as the customer said there all LED lights or cameras that are plugged into the sockets so they don't require much at all.

Is there anyway this would ok? the customer asked me to check as he said when the electrician first wired it he was 'hot' on his regs. if not would it be best putting a code 2 down on cert?

Thanks,
Carl
 
Last edited by a moderator:
That's fine, as long as the floor area covered is no more than 50m².
Have a look at Appendix 15 in BS7671.
 
agree. a 20A radial is OK.
 
Thanks, I've always been told thats a no go but just checked my regs and it's fine.

Feel abit silly now ha!
 
Hello,

I'm glad I've found this forum :)

I'm doing PIR for a customer and everything was going fine until I saw there was one 2.5mm cable leaving from consumer unit to feed 4 sockets.

The cable leaves the consumer unit and the passes threw a double pole isolator switch, it was wired this was so they could control effects lights.

At the consumer unit the radial is on a 20A MCB.

Now as the customer said there all LED lights or cameras that are plugged into the sockets so they don't require much at all.

Is there anyway this would ok? the customer asked me to check as he said when the electrician first wired it he was 'hot' on his regs. if not would it be best putting a code 2 down on cert?

Thanks,
Carl

sounds fine. what reasons do you see to think it is not?
 
Wouldn't be acceptable with a 30/32A CPD.
20A or less is fine, correction factors for installation methods permitting.
 
Hawk81, when I was an apprentice my boss always told me that it's not right, now I wonder how many times we must have ran new cables into make it a ring... when I see my ex boss I'm gonna ask him if he knows about this.

Thanks alot for the help :)
 
Hawk81, when I was an apprentice my boss always told me that it's not right, now I wonder how many times we must have ran new cables into make it a ring... when I see my ex boss I'm gonna ask him if he knows about this.

Thanks alot for the help :)

I agree you should definitely question your ex boss. Radial circuits are a very basic and simple way of wiring sockets and many prefer to do it this way. It is taught in first year in college.
 
I agree you should definitely question your ex boss. Radial circuits are a very basic and simple way of wiring sockets and many prefer to do it this way. It is taught in first year in college.


That's because a radial is better, and safer!!

:cool:
 
You mentioned an MCB but not RCD or RCBO protection. Would definatly recomend RCD protection. Check out reg 411.3.3??
 
shall we start a radial appreciation society?
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Radial Circuit
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
26

Advert

Thread statistics

Created
Carlos_tlewis,
Last reply from
Deleted member 26818,
Replies
26
Views
7,064

Advert

Back
Top