R

ryanryan

Please confirm..
On the test sheet, it is the x1 worst result that gets put on the sheet?:confused:

thanks
 
My understanding is that you record the relevant time on the certificate.
So if an RCD is being used only for fault protection i.e. meeting disconnection times where Zs is too high for MCB. Then the relevant time will be 1x.
If an RCD is providing supplementary protection (which is usually the case for 30mA units) then the relevant figure is the 5x reading.

So in the case of a 17th Edition board on a TN-S or TN-C-S system the RCD's will be supplementary so 5x is the important one.
 
hmmm.

I thought you had to do all six tests, regardless of what system its used in and what its used for.

I think you may find GN3 specifically asks for all of them.

Not got it to hand at the mo.
 
Last edited by a moderator:
My understanding is that you record the relevant time on the certificate.

All tests do need to be carried out :rolleyes:

Just to clarify I dont have a problem with recording all test results. I just wanted to point out the relevant one in a particular senario
 
Last edited by a moderator:

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Recording RCD test results
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
5

Advert

Thread statistics

Created
ryanryan,
Last reply from
xraytek,
Replies
5
Views
13,106

Advert

Back
Top