Hi peeps,

I need to remove some split core CT's from a school's Main Tails. The installers never used a shorting block but did earth the secondaries in the meter. I have tried unclipping the CT's but the magnets aren't releasing.

Can one of you kind people please advise me as to how I can get them off. Turning the supply off is not an option at this time.

I must add that this is an unofficial export meter that was installed a solar panel company.

Regards
Mark
 
Last edited:
I haven't seen the installation myself so I can't guarantee anything over the forum, but yes. Even when powered down the meter will still keep the secondary of the CT as a closed loop.

It's only when the secondary goes open circuit that high voltages can become present.

If the CT has been overheating badly as you have suggested, it could well be possible the plastic surrounding the CT could have warped, possibly causing them to be difficult to remove.
 
Thanks mate,

I had a look at them yesterday, they seem in tact and warm to the touch but not scoulding hot. I will power down this evening and remove them. Just to clarify once powered down I should just be able to unclip them immediately?

Thanks for your help, much appreciated.
 
......If the CT has been overheating badly as you have suggested, it could well be possible the plastic surrounding the CT could have warped, possibly causing them to be difficult to remove.
This was also my thinking, unless there's a hidden fixing I couldn't see any other reason they'd be difficult even when under load.

I'm glad you arranged to power down Mark, it's far safer. Did you managed to get them off without a hitch?
 
Thanks for all the support guys.

The school has now asked that I put correct size CT's on this meter and looking at the current setup it looks as if the main incomers are fused as follows:
Red - 300A
Yellow - 500A
Blue - 300A

Now my question is do I size them all at 500:5 or can I use different ratio's ie. Red - 300:5 Yellow 500:5 and Blue 300:5?

Thanks again.
 
Depends on what the power meter can be set up to, some can accept different ratios, others can't.

Personally as this isn't a high accuracy situation I'd fit 3 500:5.

Did you find why they were difficult to remove?
 
Hi RoB2

I have no idea, as soon as I powered down I was able to split them with no hassle. I gave them a good once over and there is no warping ect. It was mentioned in an earlier post about an overload magnetic circuit.
R533063-01.jpg
These are what were on there they are made by HOBUT

Thanks for your help, I was thinking down the same lines of 500:5 and as you say it's not a high accuracy situation, so 500:5 it is.

Cheers
Mark
 

Reply to Removing Split Core CT's in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock