All I can say is... subjectively it's wrong. Objectively it complies with the regulations, if you disagree and would like to convince me otherwise, please explain (a) how it violates the figure 8 test (the purpose of which is to look for interconnections between the legs of the ring at a point other than the origin, interconnections that could if ill-informed alterations were made result in a situation with the potential to overload a cable) and (b) which regulations it violates and why.

It's wrong, we all know it's wrong... explaining why with actual regulations is a little trickier. Please don't cite Appendix 15 (Informative)... it is not a regulation. Without wanting to offend, it's the regulations equivalent of 'The dummies guide to the ring final circuit as defined by regulation 433.1.204'. It provides a lot of compliant examples, but listing all possibilities would be an impossibility which is why it's informative, it's a quick start guide if you will. As best as I can tell the only actual regulation specifically about 32A ring circuits is 433.1.204, it's entirely possible I've missed some but I've looked hard whilst writing some of my replies to this thread because I wanted to be certain I was objectively correct, but I'm all ears if I've missed some.

Maybe we should look at this another way... how would you code this arrangement if you came across it on an EICR? Which regulations would you cite as those it breaks and why?

Remember... I'm really just playing devil's advocate but I am getting a little tired of late of the blind following of rules. The regulations are the bare minimum, we need to be able to think for ourselves, so if you feel like telling me which code Codebreakers applies to this situation, go right ahead and explain what justifies such a code, backing your explanation up with actual regulations and how the arrangement breaks them.

And for another fun exercise in analysing the twisted mind of this old bint... lets suppose I have a ring circuit and I ran out of 2.5mm on the job, only got an off cut left that's about 18 inches long, only had two more double sockets to sort out... kitchen job, all the cables clipped direct or in the void of a dot and dab wall, so I run a length of 6mm from a convenient place (before anyone asks how I managed to squeeze 2 x 2.5mm and 1 x 6mm in accessory terminals.. I love the new 3 way slimline Wago connectors that take 0.5mm to 6mm cable.. awesome for this kind of thinking... nice maintenance free Wagobox tucked out the way, great it was) to the first of the doubles and as they are next to each other, I use the off cut of 2.5mm to supply the other. Does that comply with the design criteria for a ring circuit supplied by a 32A OCPD? If not, why not? And if this complies... how does the situation described in the OP not?
 
All I can say is... subjectively it's wrong. Objectively it complies with the regulations, if you disagree and would like to convince me otherwise, please explain (a) how it violates the figure 8 test (the purpose of which is to look for interconnections between the legs of the ring at a point other than the origin, interconnections that could if ill-informed alterations were made result in a situation with the potential to overload a cable) and (b) which regulations it violates and why.

It's wrong, we all know it's wrong... explaining why with actual regulations is a little trickier. Please don't cite Appendix 15 (Informative)... it is not a regulation. Without wanting to offend, it's the regulations equivalent of 'The dummies guide to the ring final circuit as defined by regulation 433.1.204'. It provides a lot of compliant examples, but listing all possibilities would be an impossibility which is why it's informative, it's a quick start guide if you will. As best as I can tell the only actual regulation specifically about 32A ring circuits is 433.1.204, it's entirely possible I've missed some but I've looked hard whilst writing some of my replies to this thread because I wanted to be certain I was objectively correct, but I'm all ears if I've missed some.

Maybe we should look at this another way... how would you code this arrangement if you came across it on an EICR? Which regulations would you cite as those it breaks and why?

Remember... I'm really just playing devil's advocate but I am getting a little tired of late of the blind following of rules. The regulations are the bare minimum, we need to be able to think for ourselves, so if you feel like telling me which code Codebreakers applies to this situation, go right ahead and explain what justifies such a code, backing your explanation up with actual regulations and how the arrangement breaks them.

And for another fun exercise in analysing the twisted mind of this old bint... lets suppose I have a ring circuit and I ran out of 2.5mm on the job, only got an off cut left that's about 18 inches long, only had two more double sockets to sort out... kitchen job, all the cables clipped direct or in the void of a dot and dab wall, so I run a length of 6mm from a convenient place (before anyone asks how I managed to squeeze 2 x 2.5mm and 1 x 6mm in accessory terminals.. I love the new 3 way slimline Wago connectors that take 0.5mm to 6mm cable.. awesome for this kind of thinking... nice maintenance free Wagobox tucked out the way, great it was) to the first of the doubles and as they are next to each other, I use the off cut of 2.5mm to supply the other. Does that comply with the design criteria for a ring circuit supplied by a 32A OCPD? If not, why not? And if this complies... how does the situation described in the OP not?
 
Well if you could join the 2.5 ring to a 6.0 (or 4.0) radial, so long as it`s substantially half way around the ring then all the usual ring type considerations should pan out adequately. Again not elegant but hey ho. I feel the double triple or quadrouple ring is easier and just as valid as a single ring. Indeed, on one foru, I hasd a remasrk by someone saying theyd take one end of each ring asnd join them in the consumer unit thereby producing one ring. If it does not end up oversize (abnormal length) it would be OK but not an improvement though because you`ve then increased R1 +R2 from what it was (and therefore increased Zs) and you`ve increased volt drop too. If I found a two, three or 4 ringed circuit I would glance asgain but so long as all the sums add up and the connections are mechanically and electrically sound then hey ho not a defect. Not a standard circuit you`d find in regs informative appx 15 or in the OSG but nothing "wrong" with it.

Same as ""trees" branches yada yada on radials etc

Circuits can be unusual "strange" but still compliant and safe.

You could actually have a ring final with just one point on it. Again unusual and probably pointless but still compliant and safe
 
Oddly enough @JBW175 post #330 from today is shown as older than @SparkyChick post #331 from 25 Aug!

Is it wrong or dangerous? Not really.

Is it worth coding? Probably C3 as it was most likely a separate circuit added to an existing OCPD due to some other factor, so it could be improved by separating it and having another OCPD (ideally RCBOs, but that is another discussion point).
 
Oddly enough @JBW175 post #330 from today is shown as older than @SparkyChick post #331 from 25 Aug!

Is it wrong or dangerous? Not really.

Is it worth coding? Probably C3 as it was most likely a separate circuit added to an existing OCPD due to some other factor, so it could be improved by separating it and having another OCPD (ideally RCBOs, but that is another discussion point).

And there are two #331 posts.
 
I'm getting postings via my email regarding 'connecting two rings into one protective device' which appear to be linked to another thread posted back in the Jurassic period.

My final answer is that there is nothing wrong as they are still separate circuits but is it safe? and that depends on the way each circuitis loaded.
If the loading is small on both rings then it will pass unnoticed. The heavier the loading the greater the electrical stress.
 
Oddly enough @JBW175 post #330 from today is shown as older than @SparkyChick post #331 from 25 Aug!

Is it wrong or dangerous? Not really.

Is it worth coding? Probably C3 as it was most likely a separate circuit added to an existing OCPD due to some other factor, so it could be improved by separating it and having another OCPD (ideally RCBOs, but that is another discussion point).

i can see why it’s been done, looks original on a 1970’s 3 bed semi, only other 30A way was feeding the cooker.

it’s been coded C3, but the board was C2, so will get properly sorted when I put a new fully RCBO CU in along with other remedial works over the coming weeks.
 
C3 means a reg defect. If it`s not a C1 or a C2 then its a C3, but if not a defect it must NOT be coded at all.

Incorrect colour coding of conductors is one example of a C3
Well, if they're old colours, sleeve one 'ring' brown and blue.......there's your C3. ?
 
Absolutely no chance should there be 2 RFC in a 32A MCB.
If each one is safe if on 2 devices, what makes them become unsafe when put on 1?

Neither should there be a 2.5mm2 radial let alone 2,3 or 4.
There aren't.

It is covered in the regs and is further legislated against in test and inspection.
It isn't

Firstly assuming it is 2 RFC then it is in-fact an interconnected ring main which is the whole purpose of the ring final test to avoid.
But why, other than testing aggro?


The reason for avoiding is simple should either of the two rings of an interconnection become open circuit then the circuit becomes two or even four radials.
By exactly the same logic we should not have any ring finals, because if the ring is broken then the circuit becomes 2 radials.

Which also answers all other scenarios the 2.5mm2 Cables of a radial circuit on 32amp supply will become over loaded and be a potential fire hazard.
A figure-of-8 actually decreases the chances of a break leading to an overload potential.
 
My dad had his tv and video recorder into same plug. I think it would be safer than one of those cube adaptors hanging out the wall.

I've done the same in the past I must admit. In my own home. Not ideal, but as long as it is 2 small flexes and the cord grip secures them properly then not too bad.
 
If each one is safe if on 2 devices, what makes them become unsafe when put on 1?


There aren't.


It isn't


But why, other than testing aggro?



By exactly the same logic we should not have any ring finals, because if the ring is broken then the circuit becomes 2 radials.


A figure-of-8 actually decreases the chances of a break leading to an overload potential.
Afigure of 8 (meaning a bridge somewhere in the ring) means we can not be sure to which extent the current will flow in every scenario of current draw at any particular times .
The other meaning for figure of 8 is the test we deliberately do on an unknown circuit to see if such bridges exist.

If a ring is designed properly then the loading during is its lifetime is meant to approximate that current draw will not be unduly imbalanced therefore both legs of the ring might be expected to draw very very approximately similar loads.
That is achieved by placing outlets around the ring and not bunched by load x time or by concentrating heaviest loads in the middle one third portion.

Nobody would go to great lengths to actually measure such and make calculations (except for research) but any half decent contractor would take a few mins to make a mental note and perhaps alter things slightly from first idea to make current draw more equal.

That`s the point of having a ring (along with volt drop and R1 + R2) considerations.
We try to avoid much beyond imbalance exceeding 20 to 12 amps on a 32A ring.

The point of this thread on this forum is one ring final circuit (not ring main that`s an incorrect term and applies to something else). One ring final circuit normally consiste of one ring connected at the fuseway.
My ramblings however show thay 2 rings (or more) connected as one ring final circuit are not unsafe and not non compliant but hey yes it is an unusual set up. Just because it is not shown in the OSG as a standard circuit does not make it become "wrong".

Take a spur (spur meaning a branch off the ring, not a S F C U or F C U - again wrong term).
We can spur anywhere off a ring with no more than one twin socket, at any point or at any JB or at the fuseway. That leaves us with a single bit of 2.5 T & E on a 30 or 32 amp fuse or breaker. it passes on short cct and earth fauly but not on overload, the overload protection is provided by the twin socket having a max rating of 13A and the plugtops each having a 13A fuse in making 26A possible (though unlikely) drawn.
Just a note that use of those little "Death Cubes" should be avoided as a rule of thumb ( Cheapo 13a adadaptors 2 way unfused as it means you could have a total of 4 x 13amp plugtops in a twin socket) they could be plugged in at any point on the ring or spur and are best avoided.

Actually, just to be a bit naughty - what is unsafe about a large number of radials, each one having not more than one twin socket and all connected by say one 32A MCB. Not actually unsafe proving the joints are reliable both electrically and mechanically and all volt drop and Zs are catered for.
I wouldn`t like to see it but it would not cause piles of dead bodies to litter the place.
 
If I start with this:

1617360076641.png


and add a loop like this:

1617360138941.png


or if I start with this:

1617360198264.png


and add a link across the middle to end up with the same figure of 8, which cable(s) become at risk of being overloaded that would not if I'd done this:

1617360486923.png


?


The more paths there are for current to flow to each point of loading the less flows in any given one, not more.

Ignoring the practical realities of actually wiring it, a "full mesh" topology of interconnections

1617360838697.png


would minimise the current flowing in every single cable (apart, obv, from the ones from the OPD to the "first" and "last" sockets, but those cables are never affected by any interconnection topology anyway).

And the more connections you have the harder it becomes to turn the circuit into radials, or to create multi-socket branches, by cutting connections.
 

Attachments

  • 1617359929031.png
    28.5 KB · Views: 5
Soi disant,
Nice diagrams and well put.
Yes I like it.

Ok the point I was making.

With a bridge that makes a ring final become a "fig 8" it means that we tend to lose control of which leg gets more of the current x usage factor. A I said we don`t usually go to great lengths do control this however we do a quick approx to see if it looks badly slanted in favour of one leg or the other and then perhaps re-adjust our plan in order to balance it up a bit. This helps with heating issues and therefore aging of cables and helps reduce overloads of cables.

I`m not suggesting that fig 8 or indeed that lovely matrix thingy you drew for use is going to cause fires and threaten life everytime it`s used, far from it.

It is complicated enough to make predictions even with a well designed ring final and the fig 8/matrix complicates this further.
In reality, much of the time, no great problems should arise from it and if every ring final was done that way I don`t think we`d find streets littered with dead bodies.

However, of all the differing combinations of power drawn at various points around the ring then this arrangement is far more difficult to follow, calculate and therefore enjoy the most reasonable aspects of ring benefits as originally conceived for current flow considerations. It also makes it difficut to test properly too (OK that one can be said, to a degree, about the 2, 3, 4, umpteen rings on one ring final circuit too!)
 
It's testing which is the problem, I think. Without the predictability/consistency of readings from a proper, single, ring it's harder to spot problems such as multiple socket spurs.

But as for loading and balance - I won't mind if I prove myself wrong with some worked examples, (or if someone else does to save me the effort ?), but my initial feeling is that any cross-connections which make a figure of 8 or anything else just add current paths and thus lower the current flowing in them, not increase it.

I can sort of envisage a scenario where a section near the origin of the ring could become unbalanced, but I'm not sure how improbable it is. Need to do some sketches.

Anyone out there with circuit design software which could be used to analyse different scenarios?
 
It's testing which is the problem, I think. Without the predictability/consistency of readings from a proper, single, ring it's harder to spot problems such as multiple socket spurs.

But as for loading and balance - I won't mind if I prove myself wrong with some worked examples, (or if someone else does to save me the effort ?), but my initial feeling is that any cross-connections which make a figure of 8 or anything else just add current paths and thus lower the current flowing in them, not increase it.

I can sort of envisage a scenario where a section near the origin of the ring could become unbalanced, but I'm not sure how improbable it is. Need to do some sketches.

Anyone out there with circuit design software which could be used to analyse different scenarios?
Not really other than it's not called a ring main a ring main is a distribution circuit it's ring final circuit if you get your terms correct you may get some better responses
 
If I start with this:

View attachment 84116

and add a loop like this:

View attachment 84117

or if I start with this:

View attachment 84118

and add a link across the middle to end up with the same figure of 8, which cable(s) become at risk of being overloaded that would not if I'd done this:

View attachment 84122

?


The more paths there are for current to flow to each point of loading the less flows in any given one, not more.

Ignoring the practical realities of actually wiring it, a "full mesh" topology of interconnections

View attachment 84124

would minimise the current flowing in every single cable (apart, obv, from the ones from the OPD to the "first" and "last" sockets, but those cables are never affected by any interconnection topology anyway).

And the more connections you have the harder it becomes to turn the circuit into radials, or to create multi-socket branches, by cutting connections.
youneed to get out more. don't the pubs open soon?
 

Reply to Ring main. in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top