Not necessarily.

BS7671:2008 Amdt 2011, 514.13.1 (iii): "A durable label .... shall be fixed ... at ... the main earth terminal, where separate from main switchgear."

So, if it's adjacent to the main board, head, meter, etc, I would say no. After all, how many PME earth terminals do you see with a label?
 
i would say yes as the MET is separate from the main switchgear which is inside the CU.
 
Yep has to have one I use the yellow and black stickers, but you could just use the metal label off a BS951 earth clamp
Tel is spot on as usual
 