Where have you got that from? I said:
"Don't forget we have a regulation in the glorious 17th that recommends we consider proving a neutral at all switch locations, just in case someone wants to waste their money on some over complicated electronic switching nonsense."Now how on earth have you read that as saying you MUST do something?
Regulation 559.6.1.100:
"Consideration should be given to the provision of the neutral conductor, at each switch position , to facilitate the installation of electronic switching devices."
It does not say you must wire using a method of looping in at the switches, and it also doesn't limi it to domestic.
"Don't forget we have a regulation in the glorious 17th that recommends we consider proving a neutral at all switch locations, just in case someone wants to waste their money on some over complicated electronic switching nonsense."Now how on earth have you read that as saying you MUST do something?
Regulation 559.6.1.100:
"Consideration should be given to the provision of the neutral conductor, at each switch position , to facilitate the installation of electronic switching devices."
It does not say you must wire using a method of looping in at the switches, and it also doesn't limi it to domestic.