I have come to this forum because what I have been told my the company that fitted my system does not tally with how I understand PV solar works. I received an informative response to my previous post so I defer to you again.

I have a 4kw system with a Mastervolt 5500 inverter. Since the system was installed in November, I have had the mains trip out at least a dozen times. In the 5 years prior since building our house the mains tripped out twice due to a dodgy iron. I asked the installation company to investigate, and 4 months down the line they came to have a look.

The symptoms were quite random. The RCD on the board (80A 30mA) would trip and if I tried to reset it it would not let me, unless I reset the PV fuse. I have an audio amp that I originally thought was the cause but the electricity kept tripping. The one thing that caused me to rule out the PV originally was that it did trip a couple of times at 4 o'clock in the morning, however the same reset on the PV fuse rectified the problem in the middle of the night

The solar electrician came out this week and did a test by plugging a monitor into a 13A socket and quickly determined it was a faulty RCD. I purchased a relatively expensive new RCD and fitted it yesterday. This morning the mains tripped again. I tried to reset the RCD but it was having none of it. I turned off the isolation switch to the board from the PV and the RCD reset. I turned the isolation back on and the RCD tripped so in my mind it seems there is some issue with the incoming solar feed. At the same time this happened, I had the kettle on which may be a factor somewhere in the mix.

Any guidance/advice greatly appreciated.
 
It sounds like your system is wired wrong.
A PV system should not be on a shared RCD, so if your PV system is tripping the main RCD it must be wired in the wrong side of it.
There have been many long threads on this very point.
A PV system should be on its own RCD if one is needed at all.
I hope this helps.
 
Earthstore is right. The PV system should not be on a communal RCD. This is actually a fairly common error (one which I have made myself :aureola:) and it will probably need sorting.

If the install requires an RCD then it should really be a 100mA one. Of course, it is a little nit more complicated than that.....
 
I'm assumig that the RCD is covering the solar pv circuit as well as other household circuits?
If above is correct - I would suggest that the solar pv breaker is seperated from the main consumer unit. Get a small garage board fitted connecting directly into the tails prior to the consumer unit via a henley block.
This is isolate the tripping problem from the household circuits. It is not ideal the solar pv sharing an RCD as the solar pv will have residual current and this coupled with any residual current already existing on the household circuits could well be enough to cross the tripping threashold of the 30mA RCD.
Assuming you do the above and it turns out that the main house RCD still trips this clearly shows its a fault on the existing household circuits / and appliance connected. It wouldn't take much to narrow down the problem with use of a low resolution clamp meter.
I suspect that the test you described had been completed was a ramp test at a socket outlet. The electrician may have done this and because the RCD tripped in less than 30mA then they assumed RCD faulty. If so it wouldn't have proved much as it wouldn't have taken into account existing residual current.
 
Here's the meter & RCD. PV fuse on left side of board if you can't read it. photo1.jpg
 
Looks to be fed from the main CU via shared RCD. What type of cable is that used between the CU and the meter / AC isolator?
 
The cable looks like standard PV cable to me. I wonder if the AC isolator has a CPC to it?

The issue with the PV being fed from the shared isn't just nuisance tripping. It will also affect disconnection times.

If there is a fault of one of the circuits which are protected by the RCD, say for example the sockets, then the RCD will operate yet the PV system will still be feeding power to the circuit.
 
Does your current comsumer unit have two RCD units? Or just the one?

If it is just the one, and the method of installation allows it, the installer could simply move the circuit to the other side of the board - looking at your picture, there appears to be a spare way.
 
Just a thought on the cable that was used, it is possible that it will have a high voltage drop, which is making your system go overvoltage, and tripping the RCD which sounds like it is wired up wrong anyway.
 
Does your current comsumer unit have two RCD units? Or just the one?

If it is just the one, and the method of installation allows it, the installer could simply move the circuit to the other side of the board - looking at your picture, there appears to be a spare way.

The unit has 1 RCD.. photo2.JPG
 
Just a thought on the cable that was used, it is possible that it will have a high voltage drop, which is making your system go overvoltage, and tripping the RCD which sounds like it is wired up wrong anyway.

The cable from the inverter (in the loft) down to the export meter in the photo, or the cable from the meter into the consumer unit?
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Solar system tripping out mains.
Prefix
N/A
Forum
Solar PV Forum | Solar Panels Forum
Start date
Last reply date
Replies
47

Advert

Thread statistics

Created
lennyg,
Last reply from
moggy1968,
Replies
47
Views
34,872

Advert

Back
Top