dear fellow indulgers of the electrical disaplin, i would greatly value any ideas.

customers MCB for kitchen sockets tripped during the storm yesterday, and would not latch in for the custmer at the time. however on arival this morning, the breaker reset. all tests came out clear apart from the RCD trip time, both x1 and x5 tests triped without giving a milli second value. tried at 0 and 180, also tried at x1/2 same thing RCD tripped with no value displayed. strange as RCD hadnt rtipped with the origional fault

sockets are back on, and customer is happy, but i am not. would apreciate your thoughts.
 
was an elec storm yes, no earth leakage, all other tests ok, the RCD hadnt triped origionaly, just the MCB, but did an RCD test as part of the course, which is when it kept tripping with no values showing on tester.
 
I'd have thought that the two most obvious contenders are, er, obvious:

1) water penetration somewhere
2) power surge / emf spike

why the RCD is now being a bit suss could be because it's now shafted (not beyond possibility it could be burnt out internally hence not tripping last night - if it's only a standard 6kA one that's nothing to a bolt of lightning)
 
Could also depend on when the customer last tested the RCD, as we know they get tested every three months...
 
customer is happy, but sparky isn't. i would advise replacing the RCD and then doing a RCD test, if similar results to the old one, then there is a circuit problem
 
Hi sparky, Did you remember to conduct the RCD tests with ALL loads disconnected from the RCD. A low impedance load on the RCD may drag the voltage down so quickly, that although the RCD trips, the meter is either unable to record & display a value or displays an unreliable short disconnection time. Conversely, in situations where the load has input capacitors (eg. RFI Suppression or reservoir capacitors) the voltage maybe artificially held up, causing the meter to display an unreliable long disconnection time.
 

Reply to storm tripping in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
My thoughts exactly! Snowed under with work at the moment, so might have to pass it on 😬😬
Replies
4
Views
1K
  • Question
I have a similar issue. In my case part of the problem is the cumulative residual current across different circuits protected by a single rod. I...
Replies
7
Views
2K
  • Question
I have found it OK, but if you are happy to spend more than that also looks like a good deal.
    • Like
Replies
18
Views
2K
  • Question
Correct. And it's likely from your description that all is in fact in order. You are getting readings currently that are confusing for you, which...
Replies
4
Views
2K
  • Question
Yes its actually me doing the misinterpreting
2
Replies
31
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks