If when carrying out a "whole instalation" test from L+N to Earth the result is say 50 Megohms, and there are ,say,5 circuits would that mean that ALL the circuits pass the test or do each one still need testing?
If you have 50 meg on a global then you don't need to test further. All 5 of those circuits will individually be greater than that figure due to them being parallel resistances when tested together. BS7671 states 1 meg as minimum, not 10.
A Global IR test shows up the lowest result for the weakest insulation on a certain circuit
Yes , thats what i said. as there are 5 circuits the each one can be no lower than 50 megs? would each individual circuit still need testing?
Im talking about the real world here ...
Parellel resistances will show lower than and individual cct reading. Also I would be happy with 50 meg on a globalA Global IR test shows up the lowest result for the weakest insulation on a certain circuit. Do an IR test on each circuit and find out which one is low and then find out why?
Global IR testing is fine but when something pops up, it i time to test each circuit.
A Global IR test shows up the lowest result for the weakest insulation on a certain circuit. Do an IR test on each circuit and find out which one is low and then find out why?
Global IR testing is fine but when something pops up, it i time to test each circuit.
ps, drop the attitude.
It definately has a place in quickly confirming if an installation has an acceptable insulation value overall.Personally I'm not happy with a global test
It definately has a place in quickly confirming if an installation has an acceptable insulation value overall.
Don't understand that really. It can confirm if an installation has satisfactory insulation resistance overall and if it complies with minimum acceptable values in BS7671. Pretty useful I think.Which is about as helpful as a chocolate fireguard!
Don't understand that really. It can confirm if an installation has satisfactory insulation resistance overall and if it complies with minimum acceptable values in BS7671. Pretty useful I think.