- Reaction score
- 138
If when carrying out a "whole instalation" test from L+N to Earth the result is say 50 Megohms, and there are ,say,5 circuits would that mean that ALL the circuits pass the test or do each one still need testing?
Discuss Stupid question? Re. Insulation resistance in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
If you have 50 meg on a global then you don't need to test further. All 5 of those circuits will individually be greater than that figure due to them being parallel resistances when tested together. BS7671 states 1 meg as minimum, not 10.
A Global IR test shows up the lowest result for the weakest insulation on a certain circuit
Yes , thats what i said. as there are 5 circuits the each one can be no lower than 50 megs? would each individual circuit still need testing?
Im talking about the real world here ...
Parellel resistances will show lower than and individual cct reading. Also I would be happy with 50 meg on a globalA Global IR test shows up the lowest result for the weakest insulation on a certain circuit. Do an IR test on each circuit and find out which one is low and then find out why?
Global IR testing is fine but when something pops up, it i time to test each circuit.
ps, drop the attitude.
It definately has a place in quickly confirming if an installation has an acceptable insulation value overall.Personally I'm not happy with a global test
Don't understand that really. It can confirm if an installation has satisfactory insulation resistance overall and if it complies with minimum acceptable values in BS7671. Pretty useful I think.Which is about as helpful as a chocolate fireguard!
I know the value of individual circuit testing and don't disagree with your points above. BS7671 is the regulations though, so compliance with that is all that is required. Anymore than that is our personal preferences.It tells you if the installation meets an arbitrary value in the book without any regard for the situation.
An installation with 5 circuits could have an IR of 2 megohms and bee deemed satisfactory, and an installation of 50 circuits could have the same IR and be deemed satisfactory. It doesn't take much thinking to realise that the smaller installation is in a poorer condition, but both pass?
And what does it tell you when you look back at previous test results? Absolutely nothing as you cannot see which circuits are deteriorating and which are not.
Once upon a time the minimum value of IR was calculated based on the specifics of an installation, either from the full load current or the number of circuits/points, which makes sense as then it is related to the size of the installation.
But following a blanket 1megohm rule is just daft and symptomatic of the constant simplification of the trade to suit the lowest common denominator instead of striving to achieve a good standard
Sorry, didnt mean to be offensive... Thanks for the reply...
Yeah especially with cheap EICR's. lolIt definately has a place in quickly confirming if an installation has an acceptable insulation value overall.
Based on your global reading you can determine if individual circuit testing is required. That is what differentiates an electrician who understands the results and one that doesn't.Yeah especially with cheap EICR's. lol
I'm talking about the real world too, it's just a simple network of five resistances in parallel. It could be five circuits with 250megohm each, or any other combination of resistances which totals 50
are you absolutely sure about this dave ? If each circuit had a i.r. Of 250 megohms i think that's what you'd see on the 'global' test....
Are you absolutely sure about this Dave ? If each circuit had a I.R. of 250 Megohms I think that's what you'd see on the 'Global' test....
1/rt = 1/r1 + 1/r2 ?
I don't doubt you're all correct but we're talking about insulation resistance or integrity so maintain that if every circuit [4 circuits for example] IR tested say >200 Megohms you'd also see similar as a 'global' reading.
Does that mean the lowest IR reading the OP would get if he measured the 5 circuits separately would be 50MΩ ?e.g. if you had five circuits with very high insulation resistance and one circuit with an IR of 2MΩ, then the total resistance when measured as a "whole installation" would be less than 2MΩ.
Sorry confused.com
Reply to Stupid question? Re. Insulation resistance in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net