Guest viewing is limited
So I have a consumer unit to change, the consumer unit was in the garage but it has been converted to living accommodation years ago. The utility cupboard is on the outside wall, the consumer unit is obviously on the inside wall but near the ceiling.
The issue is when they changed the garage to living accommodation they created a second skin using breeze blocks. The tails from the utility cupboard were run in the cavity wall between the meter cupboard and the consumer unit, these tails need upgrading to 25mm plus 16mm earth.
I know just running new tails in the cavity will not provide enough protection, the cables would be less than 3m so from a DNO point of view thats fine. Its going to be hard enough to run the 25mm cables through and up the cavity wall let alone put any sort of copex to protect it, the alternative is 25mm 3 core SWA however then would need a fused isolator box in the meter box to terminate. (Can't find any sort of wiska box that would be able to make connection from tails to 25mm 3 core SWA).
Im sure I am not the first to come up against this issue so thought I would see what others thoughts were.
I don’t think it’s an issue to utilise the ‘existing’ tails set up so long as the are the correct size csa
However
If like you , they need to replace the tails I don’t think pulling up in the cavity will be acceptable practice nowadays due to lack of rcd protection
The only issue I feel with dragging any cable in a cavity, is damage being done to the cable unseen. Before anyone says anything, the bit coming out the end, may have missed the cavity tie etc, but the bit inside may have not.
That said, I I've pulled meter tails through a cavity over a short distance (less than metre) in flexible conduit. If it goes in freely, should be okay o_O
if tails are 16mm, i'd leave them alone (apart from connecting up to your new CU.). tin hat on.
Its TN-C-S with 100amp cutout fuse (Although might only be a 60 or 80 amp fuse in the carrier but says 100amp so have to presume). Tails look really small, have not taken it apart but looked at next doors that had been cut off and I would say they are 10mm tails so really need upgrading. I thought the regs say they only need RCD protection if more than 3 meters, cable length will not be more than 3 meters, but thought there had to be some mechanical protections.
How about a large wiska box with a couple of henley blocks inside to make connection between tails and swa?
Saying that trying to get even 2 core 25mm SWA though the cavity could be a problem so may not have a lot of choice.
My guess is that the consumer unit was just the other side of the wall so was not an issue but when they did the conversion the cut all the twin and earth shorter and moved the cables up and put the consumer unit at the top so it did not get damaged... It was either done by a cowboy builder or a very long time ago as its an old wylex rewireable consumer unit.
If you think that tails need rcd protection for being over 3 meters you better read again.
Why would you even think that?
Sorry yes over current protection is required was from reading an above post not RCD, this is a requirement from DNO if tails are longer than 3m.
My alternative is run the cables straight through the wall then use trunking up to consumer unit but dont think that would go down too well with customer.
You can get some 50mm double walled pvc copex which would protect the cables from installation damage at least
Its a 3 bed semi so maximum load not going to be massive but they do want to add power to an outbuilding. 10mm tails really should be replaced imo. I know the OSG says 25mm but 16mm for most would be ok but 10mm is probably pushing it a bit too much.
I think it will be a case of do what I can but think just getting 25mm tails through the cavity will be enough of a challenge let alone thinking about anything else.. The regs are all very well but in the real world...
On a TNCS or TNS system 16mm tails are ok with a 100A cut out fuse providing the installation meets the following 2 criteria:
1. Max demand of the installation (taking into account diversity) should not exceed the CCC of the 16mm tails.
2. Regulation 434.5.2 has to be met (i.e protection of the tails against fault current).
This regulation will always be met on a TNCS system as long as Ze<0.35Ω which it should be.
It will be met on a TNS system is Ze<0.48Ω as at that value K²S²>I²t (just!)
Could you not put some sort of trunking/conduit on the outside of the building, up from the services box? Or if you're going to use SWA, run that up the outside clipped direct then straight through the wall to the back of the DB.
I agree with that. I have looked into using the copex before but always come up with a different solution as I just think it would be a right pain and expensive. I usually use 25mm conduit on the outside of the wall. 2 x 25mm and 1 x 16mm just squeeze in. For a longer run you may need 32mm conduit which would be a pain as its not as easy to buy all the bits that go with it.
Is this unacceptable for meter tails >3m in a cavity wall/ceiling as per the regs ?.
Saw a client today who wanted to move some sockets. Installation about 3 years old but with no certificate or labels on the CU.
25mm meter tails ran in cavity of wall/ceiling for around 4m to the CU.
Tails ran from a double pole isolator.
Hi - I’m always happy to learn, but I don’t see a reg in BS7671 that says you can’t run cables in a building void, with greater than 50mm cover, properly done with no installation damage etc. I don’t do it, but there’s tons of homes with tails done that way.
If I was there to install outlets they’d be done by now :) .
This was the board the tails were fed into. No fire barrier were the cables enter the CU at the back either albeit installed recently. Looks like the IP rating is not too good either with all that white paint
so to protect the tails with an rcd may prove very inconvenient if there is a fault which would wipe out all of the board, but this has to be weighed up against the risk of tails in cavity/ceiling <50mm
Why do the tails need RCD protection, if they are run in a cavity, or have I missed a pertinent post again?
Fire barrier; would it not be just the meter tails coming out of the cavity, that would require sealing?
I could only see the start of the run from the DB back to the cut out which was less than 50mm.
I suppose the problem is that as I can not see the run as a whole Im not sure what is less than 50 and whats more than 50mm.
Albeit not ideal a RCD main switch would offer protection ?
So you looked at the tails next door to establish what is required in the house you are working on?
I’ve re-read your OP. I think I would consider routing an swa cable from the meter box, terminating it in one of those bracket things or metal adaptable boxes, running cores straight out through suitable gland. In the meantime ask the supplier to install one of their isolators. Is the run 3 or 5 meters?
south west
United Kingdom
Tails in cavity wall
catdog1121,
Bobster,