Ok, I'm in the middle of an EICR for a client. The tails are going into the consumer unit in separate holes (It's metal, so that's against the regs), and then inside the consumer unit they have been terminated in a really shoddy way with bare copper showing. Now copper showing on the tails is a C1 outside the CU, but is it still a C1 inside the CU given you would have to remove the cover before risking an electric shock ?
 

Matthewd29

-
Esteemed
Arms
Reaction score
1,966
Definetly not a c1 although it is poor workmanship the terminal screw is live and can be touched whether the copper is showing or not and that does not receive a code. It does not present an immediate danger. C3 at most.
 
Reaction score
32
Ok, I'm in the middle of an EICR for a client. The tails are going into the consumer unit in separate holes (It's metal, so that's against the regs), and then inside the consumer unit they have been terminated in a really shoddy way with bare copper showing. Now copper showing on the tails is a C1 outside the CU, but is it still a C1 inside the CU given you would have to remove the cover before risking an electric shock ?
pictures please
 
Reaction score
9
How much copper ? 2 mm then nothing to worry about , 2 cm then its rough as my badgers arse
I'll post a photo tomorrow, but it's a lot, at least 1cm or more. The only place copper should be showing is at the neutral or earth bars, the bus bar should be covered. As a matter of interest the codebreakers book states any copper showing on line conductors is at least a C2
 

westward10

Admin
Mod
Esteemed
Reaction score
19,117
I'll post a photo tomorrow, but it's a lot, at least 1cm or more. The only place copper should be showing is at the neutral or earth bars, the bus bar should be covered. As a matter of interest the codebreakers book states any copper showing on line conductors is at least a C2
Aside from opinion on here and Codebreakers which is generally considered a joke what do you think and why. To compile a Report you must have enough competence and knowledge to assess the type of installation you are working on.
 

Pretty Mouth

-
Esteemed
Arms
Reaction score
1,229
The only place copper should be showing is at the neutral or earth bars, the bus bar should be covered.
Supposedly not an issue, according to BPG4:

Items that should not be listed as non-compliances with BS 7671 and do not require reporting (Mythbusting):

Absence of barriers inside a consumer unit (provided the cover is removable only with the use of a key or tool)
 